Is there a rule of thumb on how deep a power pole must be buried?

Is the burial depth more dependant on the height of the pole or the weight at the top of it(example:transformer, capacitors, etc.)?

Horizontal Ad
#68505 08/09/06 02:49 PM
Joined: Jun 2002
Posts: 58
E
Member
Weight downward on a pole is not a problem. Figuring worst case of about 600 lb./sq.in (NTS-1991) for wood, bearing on 1000 lb./sq.ft. soil (UBC, IBC); weight, even with XF's, cap's, etc. is well supported.
Resistance to overturning (lateral resistance) is a big deal. Wind load, seismic motion, and conductor tension are the factors, and must be calculated based on location (wind & seismic), soil type, and other factors that our engineers just snowed me with when I asked.
POCO's have standards that are well overdesigned for their areas and equipment, and are the closest to "rules-of-thumb" around.

#68506 08/09/06 02:56 PM
Joined: Jan 2003
Posts: 4,391
I
Moderator
You can also find that type of info out in the Linemans and Cablemans Handbook.

Some libraries have it or you can buy it.

Lineman's and Cableman's Handbook



[This message has been edited by iwire (edited 08-09-2006).]


Bob Badger
Construction & Maintenance Electrician
Massachusetts
#68507 08/09/06 05:30 PM
Joined: May 2005
Posts: 12
C
Member
I just set a 12 foot pole in a resi yard. The electrical inspector told me that ...i believe building code (not for sure now) for every 4 ft of pole you go 1ft deep. So i went 3 ft. deep seemed pretty sturdy to me.

#68508 08/09/06 06:01 PM
Joined: Apr 2004
Posts: 4
1
Junior Member
I asked the power co. that provides service in my area and they told me 10 percent of pole length plus 2 feet.

#68509 08/10/06 02:47 AM
Joined: May 2003
Posts: 2,876
E
e57 Offline
Member
I have only set a few and it was a long (15 years) time ago. 6' for a 40' pole on straight runs, turns/angles deeper.

Taller poles are deeper ~8-10'.

I think the American Electricians Handbook also has some info in it.


Mark Heller
"Well - I oughta....." -Jackie Gleason
#68510 08/10/06 05:06 AM
Joined: Jul 2002
Posts: 8,441
Likes: 4
Member
As Energy7 mentioned above,
There are a few variables involved in the seating of a pole.
There is no way that there can be a formulaic way of calculating the depth for all situations.
Depending upon where you are in the world and the soil type and so forth,
It's a mine-field, it also depends upon what you are going to use the pole for.
We have used the formula 10%+ 2ft, with standard poles and have had them fall over when the ground freezes and then thaws, causing frost-heave.
My opinion would be, ask your local PoCo Lines Division.
And don't, set the pole in concrete, you are just looking for disaster, if you get bad frost levels and the pole is under any sort of strain.

Horizontal Ad
#68511 08/10/06 09:10 AM
Joined: Dec 2000
Posts: 4,293
Member
Quote
As Energy7 mentioned above,
There are a few variables involved in the seating of a pole.

Yup, you need to take the conditions into consideration. [Linked Image]

[Linked Image]

#68512 08/10/06 03:00 PM
Joined: Aug 2001
Posts: 599
N
Member
Electure,
Let me guess. Huntington Beach a little north of the pier south of the dog beach?

#68513 08/10/06 09:16 PM
Joined: May 2003
Posts: 2,876
E
e57 Offline
Member
There are some in the Stinson/Bolinas lagoon... Hwy #1 in Marin.


Mark Heller
"Well - I oughta....." -Jackie Gleason
Page 1 of 2 1 2

Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

Member Spotlight
Alan Belson
Alan Belson
Mayenne N. France
Posts: 1,803
Joined: March 2005
Top Posters(30 Days)
Admin 3
CSS 1
Popular Topics(Views)
366,345 Are you busy
289,334 Re: Forum
267,994 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5