#68418 08/08/06 10:26 AM
Joined: Aug 2006
Posts: 2
C
Junior Member
I purchased a refurbished battery backup that uses 125V/30A single phase power from a L5-30R receptacle. The on-board breaker is replaceable on the rear and is listed at 250V/30A. The reported trip amperage is 37.5A. Will this breaker throw at 4687W (125V) or not until 9375W (250V)?


Christopher Banbury, PE
President
Ark Engineering, Inc.
PO Box 10129, Brooksville, FL 34603
22 N. Broad ST, Brooksville, FL 34601
Phone: (352) 754-2424
FAX: (352) 754-2412
www.arkengineering.net
#68419 08/08/06 01:08 PM
Joined: Nov 2000
Posts: 2,148
R
Member
The breaker doesn't care about the load watts. In its themal mode (overload) it only cares about the watts caused by the current flowing through its thermal element. These watts are based on the impedance of the thermal element and the current (amps).
Don


Don(resqcapt19)