#68056 - 07/27/06 08:26 PM Flex 90  
Gregtaylor  Offline
Member
Joined: Mar 2005
Posts: 212
Boise, Idaho, USA
Situation- 1" EMT from an MCC to a motor with 4 90 degree bends in the conduit. Changed over to flex for 24" for final connection and used a flex 90 connector at the motor. The inspector turned down the job because he says that's 5 bends in the run. If that's the interpretation I can show him thousands of violations. Any thoughts?


Work Gear for Electricians and the Trades

#68057 - 07/27/06 08:44 PM Re: Flex 90  
Roger  Offline
Member
Joined: May 2002
Posts: 1,716
N.C.
Greg, unfortunately, per the pure wording of the conduit and tubing articles where it it states
Quote
There shall not be more than the equivalent of four quarter bends (360 degrees total) between pull points, for example, conduit bodies and boxes.
the inspector is correct. You could use a condolet at the transition (if it stays accessible) and be compliant.

Roger


#68058 - 07/27/06 09:06 PM Re: Flex 90  
mister h  Offline
Member
Joined: May 2006
Posts: 20
erie, pa. usa
You may need to check out 358.26 in the NEC code. This is where the code violation was from.

Ken


ken

#68059 - 07/27/06 09:11 PM Re: Flex 90  
stamcon  Offline
Member
Joined: Mar 2001
Posts: 329
So San Francisco CA
Roger, since you can't pull through a flex 90
*, should it be included as a bend between pull points? If there were 3 90* bends in the conduit and also the flex 90*, you still wouldn't be able to pull through the completed run. Just wondering...

steve


#68060 - 07/27/06 09:47 PM Re: Flex 90  
Roger  Offline
Member
Joined: May 2002
Posts: 1,716
N.C.
Steve, very good point, and if I were the inspector I would conceed to your argument.

Roger


#68061 - 07/28/06 05:56 AM Re: Flex 90  
electure  Offline


Member
Joined: Dec 2000
Posts: 4,262
Fullerton, CA USA
Why not just use one of the 90° flex fittings with the sliding cover?
Try a Regal 9674
It adds 0° to your run.


#68062 - 07/28/06 01:54 PM Re: Flex 90  
Celtic  Offline
Member
Joined: Feb 2005
Posts: 361
NJ
Quote
Greg, unfortunately, per the pure wording of the conduit and tubing articles where it it states

:There shall not be more than the equivalent of four quarter bends (360 degrees total) between pull points, for example, conduit bodies and boxes.

the inspector is correct. You could use a condolet at the transition (if it stays accessible) and be compliant.

Roger

...BUT, the flex 90 IS a pull point [Linked Image]

[This message has been edited by Celtic (edited 07-28-2006).]

[This message has been edited by Celtic (edited 07-28-2006).]


~~ CELTIC ~~
...-= NJ =-...

#68063 - 07/28/06 02:17 PM Re: Flex 90  
gfretwell  Online Content


Member
Joined: Jul 2004
Posts: 9,142
Estero,Fl,usa
How about all the "degrees of bend" in the flex whip? Does that count too?


Greg Fretwell

#68064 - 07/28/06 07:17 PM Re: Flex 90  
Gregtaylor  Offline
Member
Joined: Mar 2005
Posts: 212
Boise, Idaho, USA
My view is that the 90 degree connector WITH A REMOVABLE BACK is a pull point just like an LB would be. I did not pull wire through it along with the other bends. I pulled out enough wire to reach the motor and fed that last 36" or so through the flex and through the connector. How many bends could there be in 24" of flex?


#68065 - 07/28/06 09:12 PM Re: Flex 90  
Peter  Offline
Member
Joined: Jun 2004
Posts: 92
San Diego
Maybe 300-18 [1999 Code] may help in this situation. "The raceway shall be permitted to be initially installed without a terminating connection at the equipment."
The handbook notes that this applies to a 90º connection to a motor.
In any case, a 90º connector is impossible to pull under any circumstances. They must be hand fed one wire at a time and it takes an hour.
Note: the degree symbol "º" is made by Alt + 167. On the number keys with Num Lock and Scroll Lock on.
~Peter


Page 1 of 2 1 2

Member Spotlight
AllClear
AllClear
Belmond Iowa US
Posts: 44
Joined: August 2005
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.018s Queries: 15 (0.003s) Memory: 0.8178 MB (Peak: 0.9941 MB) Zlib enabled. Server Time: 2017-12-17 02:31:25 UTC