#68016 - 07/26/06 11:45 PM exit/emergency light circuits...  
Attic Rat  Offline
Member
Joined: Dec 2003
Posts: 524
Bergen Co.,N.J. USA
...Hi gang,..been away for awhile,.. summer being our busiest season and all,.. Hope all's well with you all..

I'm wondering,..I was doing a commercial job, and had to install exit/emergency lighting of course,..but where in the "bible" does it say what circuits I can run from?? I remember hearing about something like if there are 2 or more lighting circuits then I can come off of one of those,..what if I came off of a receptacle circuit?? This is a gray area for me as I don't do many commercial jobs, but I would like to know so I can get it right the first time... Thanx.... [Linked Image] [Linked Image] [Linked Image] [Linked Image]
Russ..


.."if it ain't fixed,don't break it...call a Licensed Electrician"

Work Gear for Electricians and the Trades

#68017 - 07/27/06 12:46 AM Re: exit/emergency light circuits...  
Gregtaylor  Offline
Member
Joined: Mar 2005
Posts: 212
Boise, Idaho, USA
Wish I had my code book in front of me to quote from, but I know this rule. In a discrete area ( each room would be treated seperately) if there are 1 or 2 lighting circuits the exit emergency lights MUST be fed from 1 or both of those circuits. If there are 3 or more lighting circuits the exit/emergency lighting MAY be fed from one or all of them and MAY be fed from a seperate circuit for exit/emergencies only. A receptacle circuit is not acceptable unless its also a lighting circuit, which isn't likely.


#68018 - 07/27/06 04:53 AM Re: exit/emergency light circuits...  
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Greg that was pretty good from memory.

Here is part of 700.12(E)

Quote
Unit equipment shall be permanently fixed in place (i.e., not portable) and shall have all wiring to each unit installed in accordance with the requirements of any of the wiring methods in Chapter 3. Flexible cord-and-plug connection shall be permitted, provided that the cord does not exceed 900 mm (3 ft) in length. The branch circuit feeding the unit equipment shall be the same branch circuit as that serving the normal lighting in the area and connected ahead of any local switches. The branch circuit that feeds unit equipment shall be clearly identified at the distribution panel. Emergency luminaires (illumination fixtures) that obtain power from a unit equipment and are not part of the unit equipment shall be wired to the unit equipment as required by 700.9 and by one of the wiring methods of Chapter 3.

Exception: In a separate and uninterrupted area supplied by a minimum of three normal lighting circuits, a separate branch circuit for unit equipment shall be permitted if it originates from the same panelboard as that of the normal lighting circuits and is provided with a lock-on feature.


[This message has been edited by iwire (edited 07-27-2006).]


Bob Badger
Construction & Maintenance Electrician
Massachusetts


Member Spotlight
AllClear
AllClear
Belmond Iowa US
Posts: 44