#67771 - 07/14/06 05:42 PM Pump Motor v. Phase Converter  
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
A decorative fountain at a shopping center has a 3 HP, 3 Phase, 208-240 volt pump.
The control box lists 10 amps for the motor.
The "factory test" sticker shows L1 @ 6.3amps and L2 & L3 @ 5.6 amps.

Since only single phase power is available, a Phase Converter (rotary) was installed.

The converter output voltages are all about equal (230-235 volts) but the pump draws 13 amps on L1 & L2 and 7 amps on L3, which is the "manufactured" phase.

Pump company says they "don't recommend" phase converters and tweaking of the vonverter capacitors may be necessary. Phase converter company says that since voltages are good, something may be wrong with the pump. They spoke to each other for me and decided that I should try adding a 22 mFD capacitor to help.

I think the darn thing should work as is.

BTW, changing the pump is not an option.

Any thoughts?

Thanks!

[This message has been edited by Redsy (edited 07-14-2006).]


Work Gear for Electricians and the Trades

#67772 - 07/14/06 06:28 PM Re: Pump Motor v. Phase Converter  
NJwirenut  Offline
Member
Joined: Sep 2001
Posts: 806
Bergen County, NJ
Is changing just the pump MOTOR an option? Would be the simplest fix.

Why the differences in current draw between the 3 legs? Does the unit incorporate some control gear as well as the motor?


#67773 - 07/14/06 07:35 PM Re: Pump Motor v. Phase Converter  
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
Get a new pump! I wouldn't want to instal this thing without GFI protection- and that motor is plenty small to be available in single phase.

BTW, there is no way a 3 hp pump pulls only 5 amps a leg. Look at your lift and flow- I bet you can get the same results with a 1/2 hp pump.

[This message has been edited by renosteinke (edited 07-14-2006).]


#67774 - 07/14/06 07:38 PM Re: Pump Motor v. Phase Converter  
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
The whole thing is a brand new, unitized pump/fountain unit that floats in a retention basin.
It was specified and bought by the site manager, and installed in the pond by a different electrician. The phase converter was specified by an application salesperson, and installed by me.

I don't know why the current imbalance. The measurements are taken at the pump cable, and no other load is applied to the cable.

It's not a complicated installation. I believe it should work as installed, with equal current distribution.

[This message has been edited by Redsy (edited 07-14-2006).]


#67775 - 07/14/06 07:51 PM Re: Pump Motor v. Phase Converter  
SolarPowered  Offline
Member
Joined: Jul 2004
Posts: 625
Palo Alto, CA, USA
I suspect that the angle between the phases is different from the 120 degress that it should be.

Perhaps a VFD could be used to generate a good three-phase feed for it?


#67776 - 07/14/06 08:21 PM Re: Pump Motor v. Phase Converter  
LK  Offline
Member
Joined: Jan 2003
Posts: 1,429
New Jersey
If you run the pump dry, under no load, then what is the reading?


#67777 - 07/14/06 10:51 PM Re: Pump Motor v. Phase Converter  
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
Thanks for the input guys.

The unit is a UL Listed pump / aerator that comes as a package with a control cabinet, 3-phase GFCI and all the necessary controls. Replacement of components is not an option.

The converters troubleshooting guide suggests that the converter may need to be upsized, or capacitance added.

I think a mis-application has occurred.
If I was there initially, I would have insisted a single-phase unit be purchased.

I guess I'm headed to the "capacitor store".


#67778 - 07/15/06 09:19 PM Re: Pump Motor v. Phase Converter  
jraef  Offline
Member
Joined: Jul 2004
Posts: 101
San francisco, CA, USA
A VFD was the answer, even if you neve change the speed. Most VFDs 3HP and uder can accept 1 phase input and give 3 phase output without derating. I think PRCs are a waste for anything 3HP and under.


JRaef

#67779 - 07/16/06 02:39 AM Re: Pump Motor v. Phase Converter  
Scott35  Offline

Broom Pusher and
Member
Joined: Oct 2000
Posts: 2,708
Anaheim, CA. USA
Quote

The converter output voltages are all about equal (230-235 volts) but the pump draws 13 amps on L1 & L2 and 7 amps on L3, which is the "manufactured" phase.


Definitely looks like a Capacitive Reactance Tweek is needed here!

I bet the 22µF Capacitor brings the load levels on L1 and L2 down to the 10 - 11 Amps range, and the "Pseudo-Phase" L3 may drift around the 8 - 9 Amp level, which would mean it might actually start doing some work!!!

As it is now, only L1 and L2 are doing any work - L3 is kind of slacking off (insufficient KVA available).

With additional XC (Capacitive Reactance), the "Pseudo Phase" L3 can contribute more work, therefore bringing the polyphase loads more into a balance.

Just do not expect a completely balanced load value here!
The polyphase motor is being driven more from 1 phase apparent power, than polyphase apparent power.
The "Pseudo Phase" L3 does not follow the same power curves & all that silly E-lecktricul Injunearring type stuff, as the lines derived from the Transformer - and the real disappointing thing: they are still only a Single Phase!

This setup really should have been specified to use a 1 Phase 3 or 5 HP Motor - a Capacitor Start-Run type would have been a good choice too!

I realize the design and ordering of the pump equipment was in the hands of others, so maybe some "constructive critsism" should be delivered to the specifying party(s).

Something like:
"I feel sorry for that poor Motor, being subjected to that crappy power quality from the Phase Converter"
[Linked Image]

Scott35


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!

#67780 - 07/16/06 11:44 AM Re: Pump Motor v. Phase Converter  
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA



Member Spotlight
HappyElectrician
HappyElectrician
Penn USA
Posts: 31
Joined: December 2011
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.023s Queries: 14 (0.004s) Memory: 0.8119 MB (Peak: 0.9853 MB) Zlib enabled. Server Time: 2017-10-24 00:33:42 UTC