is it up to the inspector? #66379
06/01/06 01:53 AM
06/01/06 01:53 AM
D
drgnz23  Offline OP
Member
Joined: Feb 2002
Posts: 56
los angeles
Okay im doing a 200 amp service change.
(1)Does my ground have go from the panel to the main water line then to my ground rod or can i save some money and start with the ground rod first ? Considering prices are so high for coppper i dont want to back track my ground and use another 50 ft...

Work Gear for Electricians and the Trades
Re: is it up to the inspector? #66380
06/01/06 03:28 AM
06/01/06 03:28 AM
Trumpy  Offline

Member
Joined: Jul 2002
Posts: 8,250
SI,New Zealand
Did you bid too low?.

Re: is it up to the inspector? #66381
06/01/06 05:39 AM
06/01/06 05:39 AM
J
je1ff  Offline
Junior Member
Joined: Jul 2004
Posts: 1
Don't you run a seperate ground from the panel to each? You only need #6 to the rod, and you need #4 for the waterpipe.

Re: is it up to the inspector? #66382
06/01/06 06:26 AM
06/01/06 06:26 AM
S
steve ancient apprentice  Offline
Member
Joined: Mar 2005
Posts: 169
west springfield,mass
I totally agree with je1ff. #6 wire to the ground rods and # 4 to the water pipe with proper clamps to jump the meter. Have never seen it done any other way. Years ago they just ran it to the water meter but not today.

Re: is it up to the inspector? #66383
06/01/06 08:56 AM
06/01/06 08:56 AM
B
BigB  Offline
Member
Joined: Mar 2004
Posts: 734
Tucson, AZ USA
Where 2 rods are required, would it be NEC compliant to run 2 GEC's from the main bus, one to each rod?

Re: is it up to the inspector? #66384
06/01/06 09:37 AM
06/01/06 09:37 AM
R
Roger  Offline
Member
Joined: May 2002
Posts: 1,716
N.C.
You can run a propper sized (largest required for the sevice) GEC to the first electrode and use jumpers to bond all the rest together.

[Linked Image]

Although it is okay to run a seperate GEC to each GE it is not necessary, see 250.50

Roger

Re: is it up to the inspector? #66385
06/01/06 09:57 AM
06/01/06 09:57 AM
M
macmikeman  Offline
Member
Joined: Jul 2002
Posts: 717
Honolulu, Hawaii
Nice drawing Roger. May I add the word "Interior" to the blue colored note? 250.52

[This message has been edited by macmikeman (edited 06-01-2006).]

Re: is it up to the inspector? #66386
06/01/06 10:09 AM
06/01/06 10:09 AM
Bill Addiss  Offline
Member
Joined: Oct 2000
Posts: 3,903
NY, USA
For what it's worth our local POCO requires a separate GEC to each rod.

Bill

Re: is it up to the inspector? #66387
06/01/06 10:51 AM
06/01/06 10:51 AM
R
Roger  Offline
Member
Joined: May 2002
Posts: 1,716
N.C.
Thanks Mike, but I can't take the credit, the drawing is out of the handbook. [Linked Image]

As Bill points out, sometimes there are rules outside of the NEC or local electrical codes that we must follow.

Roger

Re: is it up to the inspector? #66388
06/01/06 04:39 PM
06/01/06 04:39 PM
R
Ryan_J  Offline
Moderator
Joined: Aug 2003
Posts: 1,374
West Jordan, Utah, USA
I tend to disagree with the handbook drawing in this instance. The last sentance of 250.53(D)(2) states that a supplemental electrode must be bonded to:
1) The GEC,
2) The service nuetral,
3) The service conduit, or
4) A grounded service enclosure.

One of the electrodes in the handbook drawing MUST be called a supplement, and bonding the supplemntal electrode to the water pipe is not one of the 4 options listed above, as per 250.53(D)(2).


Ryan Jackson,
Salt Lake City
Page 1 of 3 1 2 3

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
akmaster
akmaster
alaska
Posts: 70
Joined: June 2012
Show All Member Profiles 
Top Posters(30 Days)
Admin 7
Popular Topics(Views)
251,660 Are you busy
188,793 Re: Forum
178,510 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.031s Queries: 15 (0.006s) Memory: 1.0254 MB (Peak: 1.2031 MB) Zlib enabled. Server Time: 2018-11-21 11:59:18 UTC