208 v. 240... again! #65443
05/03/06 07:01 AM
05/03/06 07:01 AM
R
Redsy  Offline OP
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
We know that motors can tolerate = / - 10% voltage variation. That math is simple enough on a dual-voltage motor (230 / 460, 120 / 230).

What if the motor is rated 120 / 208-230.
What is the actual permitted deviation at the higher voltage.
Can you apply the tolerance to the whole range?
For example, supplying the motor with 240 volts would still be less than 10% above 230, but it will be more than 10% above 208.

Work Gear for Electricians and the Trades
Re: 208 v. 240... again! #65444
05/03/06 10:35 AM
05/03/06 10:35 AM
L
Larry Fine  Offline
Member
Joined: Feb 2005
Posts: 693
Richmond, VA
That means the motor will operate on any voltage within that range; in this case, anywhere between 208 and 230, as well as 10% below 208 and above 230. In my opinion, the 240 will be satisfactory.


Larry Fine
Fine Electric Co.
fineelectricco.com
Re: 208 v. 240... again! #65445
05/03/06 05:23 PM
05/03/06 05:23 PM
D
Dave T  Offline
Member
Joined: Jan 2005
Posts: 155
Waukesha, WI, USA
Remember that 240v is a nominal voltage and the actual voltage where the motor is to be most likely will be close to 230v.
How many motors are labeled 480v? Most are 460v.

Re: 208 v. 240... again! #65446
05/03/06 09:01 PM
05/03/06 09:01 PM
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
When an appliance -such as a motor- is given an operating range on the nameplate, the entire range is used.

For example, a motor rated 208-230 (on the nameplate) would have been tested at -10% of 208, and +10% of 240.

An important consideration, however, is that the testing criteria only require that nothing bad immediately happen. Long-term over-heating, inefficiency, and a dramatic loss of torque are all allowed, and not even looked for!

Re: 208 v. 240... again! #65447
05/04/06 04:55 AM
05/04/06 04:55 AM
T
Tesla  Offline
Member
Joined: Jun 2004
Posts: 1,273
Sacramento, CA
In the term of the art:

Supply/ Line voltage of 240 is considered equal to ...

Motor/ Load voltage of 230.

These terms refer to the exact same system.

208V supplies are to feed 200V motors.

All of these terms are NOMINAL.

ie they are NEVER expected to be exact. If you get close... you're okay.


Tesla
Re: 208 v. 240... again! #65448
05/04/06 11:35 AM
05/04/06 11:35 AM
S
SolarPowered  Offline
Member
Joined: Jul 2004
Posts: 625
Palo Alto, CA, USA
Dumb question: Does anything bad happen when you increase the voltage to a synchronous motor? For example, if you had a 230/240V or whatever it is motor, and ran it at, say 300V, does that cause any problems?

Motors are, obviously, different from light bulbs. Increase the voltage feeding a light bulb, and the current increases, the power increases as the square of the voltage increase (not counting the temperature dependence of the filament, which is huge), all of which results in a large increase in brightness and a very short lifetime.

A synchronous motor, on the other hand, tends to draw whatever power is needed to rotate the load. If you increase the voltage to it, it's just going to cause a slight change in the phase angle between rotating vector and the nominal "no load" position, so that after you figure in the change in power factor, it's drawing pretty much the same power as before. At least that's how is seems to me.

Beyond synchronous motors, I don't have a mental picture for other types of motors, so I don't even have a theory on how voltage effects them.

Any thoughts on any of this?


[This message has been edited by SolarPowered (edited 05-04-2006).]


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
TOOL_5150
TOOL_5150
Bay Area
Posts: 61
Joined: August 2007
Show All Member Profiles 
Top Posters(30 Days)
Admin 5
Popular Topics(Views)
248,129 Are you busy
185,587 Re: Forum
174,921 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.027s Queries: 14 (0.005s) Memory: 0.9771 MB (Peak: 1.1244 MB) Zlib enabled. Server Time: 2018-07-19 17:02:40 UTC