Large Residential HVAC Services #64423
04/07/06 02:59 PM
04/07/06 02:59 PM
R
rad74ss  Offline OP
Member
Joined: Apr 2004
Posts: 156
Pryor, OK USA
I am currently working on a series of Residential HVAC Chillers with integral pump packages. Our largest unit has the following stats. RLA=499, MCA=509, Max Fuse =600 (HACR breaker can be higher). 240/1/60 main 115/1/60 and 24/1/60 control.

Has anyone worked on residential HVAC Services this size?

We are mounting the Fused Disconnect on our unit for ease of customer installation as well.

Work Gear for Electricians and the Trades
Re: Large Residential HVAC Services #64424
04/07/06 07:08 PM
04/07/06 07:08 PM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
Rad,
Quote
Max Fuse =600 (HACR breaker can be higher).

If the label only say Max Fuse, and doesn't list a breaker size, you must use a fuse as the overcurrent protective device. The use of a breaker would be a code violation.
Don


Don(resqcapt19)
Re: Large Residential HVAC Services #64425
04/08/06 07:55 AM
04/08/06 07:55 AM
R
rad74ss  Offline OP
Member
Joined: Apr 2004
Posts: 156
Pryor, OK USA
I should have been more clear. The label says Max Fuse/Breaker*. There is a side note saying a HACR breaker must be used if compressor protection is not provided.

On these particular units we will provide both compressor fusing and a unit fused disconnect.

Some of our customers try to trim as much cost off the unit price as possible and make up for it on the service end. These units are so large and are sectional that we are going to catalog them with all the protection we can provide.

Re: Large Residential HVAC Services #64426
04/08/06 12:41 PM
04/08/06 12:41 PM
L
Larry Fine  Offline
Member
Joined: Feb 2005
Posts: 693
Richmond, VA
"Residential" and "Max Fuse =600"?????

Could this have said "60a"?


Larry Fine
Fine Electric Co.
fineelectricco.com
Re: Large Residential HVAC Services #64427
04/08/06 12:42 PM
04/08/06 12:42 PM
L
Larry Fine  Offline
Member
Joined: Feb 2005
Posts: 693
Richmond, VA
Or do you mean multi-family buildings?


Larry Fine
Fine Electric Co.
fineelectricco.com
Re: Large Residential HVAC Services #64428
04/10/06 07:56 AM
04/10/06 07:56 AM
R
rad74ss  Offline OP
Member
Joined: Apr 2004
Posts: 156
Pryor, OK USA
600 Amps is correct.

The units will be cataloged as "Estate Chiller" and are for large single residences. If it helps to narrow things down the rep is in Connecticut. We have also built several for ski lodges and wineries.

They range in capacity from twenty to sixty tons with an integral dual pump package and a DDC controller.

Personally I thought that if they can afford that, then they can afford to get a three phase connection. The upper management people who designed the theory of the unit wanted to be able to install it on pre-existing 240 single phase hookups and let the customer worry about the electric bill.

Re: Large Residential HVAC Services #64429
04/10/06 12:30 PM
04/10/06 12:30 PM
B
Bob  Offline
Member
Joined: Feb 2002
Posts: 182
Mobile, AL, USA
"Our largest unit has the following stats. RLA=499, MCA=509, Max Fuse =600 (HACR breaker can be higher). 240/1/60 main 115/1/60 and 24/1/60 control."

Does this unit have a soft start? I was looking at a RLA = 499 and a 600 amp breaker.
Also the MCA = 509 amps is too low if the
FLA is 499 amps.

Re: Large Residential HVAC Services #64430
04/10/06 12:56 PM
04/10/06 12:56 PM
R
rad74ss  Offline OP
Member
Joined: Apr 2004
Posts: 156
Pryor, OK USA
All the units except the 20HP unit are modular. Each module has a tandem set of scroll compressors and two fans. The individual compressor amps are only around 32 amps. That is why the RLA and MCA are so close. On the largest unit the pump is the largest load at 40 amps. All of the heat trace for the water piping, the GFCI outlet and pumphouse service light are on a seperate generator back up service.

The small modular scroll compressor layout saves on start up amp draw and also gets around the requirement for a full time manager. Larger screw compressors and some recips require a full time manager under some city codes.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Attic Rat
Attic Rat
Bergen Co.,N.J. USA
Posts: 524
Joined: December 2003
Show All Member Profiles 
Top Posters(30 Days)
Admin 9
Popular Topics(Views)
244,092 Are you busy
181,135 Re: Forum
171,327 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.020s Queries: 15 (0.003s) Memory: 0.9925 MB (Peak: 1.1519 MB) Zlib enabled. Server Time: 2018-02-25 23:27:50 UTC