#64298 04/04/06 09:54 PM
Can you run a 208 single phase motor of this 240/120D 3 phase service?
Dnk...
[This message has been edited by Dnkldorf (edited 04-04-2006).]
#64299 04/04/06 10:11 PM
I have always heard you shouldn't run L/N loads on a wild leg unless it was a real 3 transformer delta. It is supposed to screw up the voltage across the open side compared to the closed side.
#64300 04/04/06 11:31 PM
Bob Offline
You need to look at the motor name plate. If
the motor is rate 208/240 its ok. If not you may need to install a bucking transformer.
