two soda machines #64290
04/04/06 12:30 PM
04/04/06 12:30 PM
S
ShockMe77  Offline OP
Member
Joined: Jun 2005
Posts: 821
Rahway, New Jersey
Was curious to know if (2) soda machines set in the middle of a room could be wired with flexible cord attached to a twist-lock receptacle attached to the ceiling grid of a suspended ceiling. Would 400.7 (A)(6) cover me?

Work Gear for Electricians and the Trades
Re: two soda machines #64291
04/04/06 12:51 PM
04/04/06 12:51 PM
R
raider1  Offline
Member
Joined: Jul 2005
Posts: 46
north logan, utah, US
Also take a look at 422.16(A)

Chris

Re: two soda machines #64292
04/04/06 01:35 PM
04/04/06 01:35 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,200
Estero,Fl,usa
They may want some independent support of the box. Running an extra support wire or two should calm that fear.


Greg Fretwell
Re: two soda machines #64293
04/05/06 01:50 PM
04/05/06 01:50 PM
G
Geno  Offline
Member
Joined: Aug 2001
Posts: 16
Syracuse, NY USA
look at 422.51

Re: two soda machines #64294
04/05/06 05:40 PM
04/05/06 05:40 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 6,950
Brick, NJ USA
Shock:
'Cord' cannot be used for permanent wiring methods. That said, IF you have a vend with a cord long enough to reach your receptacle, no problem.

IF you are proposing a twistlock to cord to a 1900 box that the machine cord will plug into; that does not fly.

Dependent on the ceiling height, you may want to consider a power pole, or IMC/RGC from ceiling to floor with the recept(s) installed therein.

John


John
Re: two soda machines #64295
04/05/06 07:18 PM
04/05/06 07:18 PM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
By the way vending machines require GFCI protection if integral or by the branch circuit.

2005 - 422.51


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: two soda machines #64296
04/05/06 07:56 PM
04/05/06 07:56 PM
W
winnie  Offline
Member
Joined: Sep 2003
Posts: 649
boston, ma
Hotline1:

Wouldn't a permanently installed cord hanging from a box to a female cord cap be explicitly permitted by 400.7(A)(1)?

-Jon

Re: two soda machines #64297
04/05/06 08:59 PM
04/05/06 08:59 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,200
Estero,Fl,usa
Perhaps I missed what he was trying to do. I was thinking the receptacle was in a box, attached to the grid and it was connected with an article 300 wiring method above the ceiling (MC whip or something).


Greg Fretwell

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
RH1
RH1
California
Posts: 22
Joined: August 2009
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
245,936 Are you busy
183,030 Re: Forum
172,784 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.029s Queries: 14 (0.006s) Memory: 0.9918 MB (Peak: 1.1512 MB) Zlib enabled. Server Time: 2018-04-26 13:09:51 UTC