Understanding nameplate information. #64204
04/02/06 01:31 PM
04/02/06 01:31 PM
C
Cinner  Offline OP
Member
Joined: Dec 2004
Posts: 78
Kelowna, B.C., Canada
Can someone explain a couple of things to me on this nameplate info for a convection oven:

TOTAL KW = 5.5KW

208, 240v 3 Phase Loading - KW per Phase:
L1-L2 = 2.5, L2-L3 = 0 , L1-L3 = 3Kw

Nominal Amps per line wire:
3 Phase 208 Volt
L1 =23, L2= 10, L3=12

Why is there unbalanced loads per phase and how would you choose a cable wire size with all the different amperages? Would you base cable wire size on the largest - 23 amps? Would you use a 3 pole 30 amp breaker?

Work Gear for Electricians and the Trades
Re: Understanding nameplate information. #64205
04/02/06 01:39 PM
04/02/06 01:39 PM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
The unbalanced current is the result of single phase fan motors and controls.

Yes you must select a cord and branch circuit with at least a 23 amp capacity.

[This message has been edited by iwire (edited 04-02-2006).]


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: Understanding nameplate information. #64206
04/02/06 01:43 PM
04/02/06 01:43 PM
C
Cinner  Offline OP
Member
Joined: Dec 2004
Posts: 78
Kelowna, B.C., Canada
L2-L3 = 0 kw...why no load b/w 2 and 3?

[This message has been edited by Cinner (edited 04-02-2006).]

Re: Understanding nameplate information. #64207
04/02/06 03:35 PM
04/02/06 03:35 PM
J
JBD  Offline
Member
Joined: Jul 2001
Posts: 599
WI, USA
With no load between L2-L3 it would be very easy to convert the oven to work on a 2 wire single phase supply.

Re: Understanding nameplate information. #64208
04/03/06 01:26 AM
04/03/06 01:26 AM
C
Cinner  Offline OP
Member
Joined: Dec 2004
Posts: 78
Kelowna, B.C., Canada
would a 3 pole 30 amp breaker be sufficient?


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
dougwells
dougwells
kamloops BC Canada
Posts: 1,143
Joined: May 2003
Show All Member Profiles 
Top Posters(30 Days)
twh 12
Popular Topics(Views)
246,868 Are you busy
184,218 Re: Forum
173,458 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.022s Queries: 14 (0.004s) Memory: 0.9668 MB (Peak: 1.1067 MB) Zlib enabled. Server Time: 2018-05-22 21:36:27 UTC