Non-CTL panel #6264
12/27/01 11:40 PM
12/27/01 11:40 PM
R
Redsy  Offline OP
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
I followed up on a home inspection report today and opened up a residential 150 Amp 30 ckt panel which contained mostly mini breakers for a total of 34 branch circuits with about 8 full size spaces still open. It was not a "CTL" panel. The home inspection report noted that there was "additional capacity available". The bus diagram on the door only depicted full size breakers (one per space = 30).

Comments, please.

Work Gear for Electricians and the Trades
Re: Non-CTL panel #6265
12/28/01 08:20 AM
12/28/01 08:20 AM
electure  Offline

Member
Joined: Dec 2000
Posts: 4,274
Fullerton, CA USA
You might check on the label for the "approved" C/Bs to be used with the loadcenter to see if it allows for the use of the minis (AKA junks).
If not, it's subpanel time.
???Is a CTL required where the available fault current is low (<10KA)? (I don't know the answer to this one)

Re: Non-CTL panel #6266
12/28/01 09:56 AM
12/28/01 09:56 AM
J
JBD  Offline
Member
Joined: Jul 2001
Posts: 599
WI, USA
In this case CTL means CircuiT Limiting not current limiting. This is a UL Classification for limiting the number of circuits in a panelboard.

Circuit limiting "tandem" breakers have some type of rejection feature to prevent them being installed in non-CTL panels. "Cheater" breakers do not have these rejectors.

Re: Non-CTL panel #6267
12/28/01 04:40 PM
12/28/01 04:40 PM
S
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,360
Redsy,
was this concern part of your follow up? can you simply take advantage of the 8 open spaces??

Re: Non-CTL panel #6268
12/28/01 10:22 PM
12/28/01 10:22 PM
R
Redsy  Offline OP
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
sparky,

I'm mainly just curious about the use of mini breakers in a non-CTL panel and how many breakers can properly be installed. I'm thinking only 30 full size(no minis). Someone could conceivably install 60 mini breakers in this panel.
The reason that I was called in was because the home inspector "recommended the service be upgraded to 200 amp". What his recommendation is based on, I haven't a clue. He didn't say. Now the buyers want a 200 amp upgrade. This was immediately after his remark that "there was additional capadity available". This, I assume was due to the 8 available spaces. I did a calculation for existing dwellings and determined that about 115 amps is adequate for this size home.

Re: Non-CTL panel #6269
12/29/01 06:39 AM
12/29/01 06:39 AM
S
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,360
I see..I am also curious,
Is 'CTL' clearly defined on the panel stickers? Or is this info purseued via listing?

Re: Non-CTL panel #6270
12/29/01 10:19 AM
12/29/01 10:19 AM
F
Frank Cinker  Offline
Member
Joined: Jul 2001
Posts: 311
Pennsylvania
Redsy,

I never heard of an Inspector requiring a service upgrade without having calculations from NEC Article 220 that would justify such. Calculations from Article 220 would clearly indicate if one was needed.

Re: Non-CTL panel #6271
12/29/01 05:51 PM
12/29/01 05:51 PM
Joe Tedesco  Offline
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
Sparky: Class CTL means "circuit limiting" See Section 384-15, paragraph 2 in the 1999 NEC:

A lighting and appliance branch-circuit panelboard shall be provided with physical means to prevent the installation of more overcurrent devices than that number for which the panelboard was designed, rated, and approved.

From the UL White Book: "Class CTL panelboards are identified by the words "Class CTL" on the Underwriters Laboratories Inc. Follow-Up Service Listing Mark.

Class CTL panelboards incorporate physical features which in conjunction with the physical size, configuration, or other
means provided in Class CTL circuit breakers, fuse holders, or fusible switches, are designed to prevent the installation of
more overcurrent protective poles than that number for which the device is designed and rated."

I have images showing this information on the equipment.


Joe Tedesco, NEC Consultant
Re: Non-CTL panel #6272
12/29/01 08:13 PM
12/29/01 08:13 PM
S
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,360
Yes Joe,
my Q was if the panels are, or are required to be, marked as such.

Re: Non-CTL panel #6273
12/29/01 09:26 PM
12/29/01 09:26 PM
R
Redsy  Offline OP
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
Frank,

He's not a real electrical inspector. He's one of the "Home Inspection Service" employees. This is a popular concept in recent years in which a home buyer will pay about $300.00 to have someone give a home that they want to buy the once-over. It is just a cursory inspection of the major parts of the home. Often, they recommend a professional tradesman evaluate certain systems furhter. As I said, his "recommended upgrade" seems to be just a thought on his part because he didn't have any basis for it. Problem is, now the buyers are requesting the upgrade. The "existing dwelling" calculation falls well within the existing 150 amp service, so I can honestly say it doesn't need an upgrade. I don't like all these mini breakers in this panel. (He didn't seem to mind them). However, I was called to asses the service capacity only, not the inside of the panel. It's an awkward situation, I wish I hadn't seen the panel.

Page 1 of 3 1 2 3

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
NickD
NickD
Amish Country, PA
Posts: 46
Joined: March 2013
Show All Member Profiles 