12/3 kitchen #6178 12/25/01 02:25 PM
Joined: Jun 2001
Posts: 196
C
Cindy Offline OP
Member
Will GFCI receptacles work in the 2 small appliance branch circuits if they share a 12/3 neutral?
C

Work Gear for Electricians and the Trades
Re: 12/3 kitchen #6179 12/26/01 12:58 AM
Joined: Jun 2001
Posts: 141
A
amp-man Offline
Member
Cindy,

They'll work if you pigtail them off the hot & neutral, but not if you try to protect downstream receptacle outlets off of the load side of one GFI. So for a multi-wire circuit, it's a chicken in every pot, er, no, I mean a GFI at every outlet.

Hope your Christmas was Merry.

Cliff

Re: 12/3 kitchen #6180 12/26/01 01:32 AM
Joined: Dec 2001
Posts: 437
The Watt Doctor Offline
Member
I'm not sure what amp-man means by his reply, but I think I understand his intent. I would like to add the following. If I can, draw a picture in your mind of what I would do, and hopefully that will help you. A GFCI "monitors" the difference between current flow on the hot and neutral, and when the difference becomes more than a few milliamps it will trip.
Given the above, I would take your 12/3 nm cable (black, red, white, bare), and land it in 2 gang box. Pigtail the neutral with (2) pigtails, and land one on each of the line sides of (2) GFCI receptacles. Then land the black on the line side of one GFCI, and the red on the line side of the other GFCI. Now, feed the other small appliance outlets from the load sides of those 2 GFCI's. This will give GF protection to every outlet on the load side of those receptacles. Hope it helps Cindy.
HMEL #688


The Watt Doctor
Altura Cogen
Channelview, TX
Re: 12/3 kitchen #6181 12/26/01 08:39 AM
Joined: Dec 2000
Posts: 4,283
electure Offline
Member
And I think they both mean a 12/2 to the downstream recps. Use the 12/3 only as a homerun.

Re: 12/3 kitchen #6182 12/26/01 11:25 AM
Joined: Jun 2001
Posts: 196
C
Cindy Offline OP
Member
I haven't done this before and don't recall others doing it either. Why not? Seems like sharing the neutral is a good idea.

Re: 12/3 kitchen #6183 12/26/01 12:01 PM
Joined: Nov 2001
Posts: 280
M
motor-T Offline
Member
Cindy
A 12/3 to gfci is possible as amp-man pointed out, but I would be more inclined to use a 20 amp 2 pole gfci breaker, that way you would have the two required 20 amp small appliance circuits and they are gfcci protected, and you can run your 12-3.

Re: 12/3 kitchen #6184 12/26/01 02:37 PM
Joined: Nov 2000
Posts: 2,236
sparky66wv Offline
Member
To reiterate: 12-3 on the homeruns, downstream of GFCI's must be 12-2 or the GFCI's will perpetually nuisance trip...

The wirenut on the shared neutrals must be very well installed or the ol' "240V series" may wipe out some appliances.


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
Re: 12/3 kitchen #6185 12/26/01 07:55 PM
Joined: Dec 2001
Posts: 437
The Watt Doctor Offline
Member
Cindy,
Electure managed to say in one sentence what didn't say in several sentences. If I had it to say over again, I would say exactly what he said. Have a nice day.
HMEL #688


The Watt Doctor
Altura Cogen
Channelview, TX

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
waymag
waymag
dallas, texas, USA
Posts: 69
Joined: January 2002
Show All Member Profiles 
Top Posters(30 Days)
BigB 3
Popular Topics(Views)
270,734 Are you busy
204,965 Re: Forum
193,079 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3