What would you expect? #608 02/13/01 02:16 AM
sparky66wv Offline OP
A 20A 2 pole breaker has a load of 40 Amps line to ground on one side only. What amount of time should the breaker trip at twice it's rated load?
Several seconds is expected to reduce nuisance tripping on motor-start-up loads, but what would be considered extreme on the high end?
How fast would a 20A fuse blow under 40 Amps?
A time delay 20A fuse under 40 Amps?
At what percentage should a breaker trip within one minute? 120%? 150%? 200%?
Is there any info out there that may give me the data of what UL expects from a breaker or fuse?
-Virgil
5 Star Inspections
Member IAEI
Re: What would you expect? #609 02/13/01 11:59 AM
resqcapt19 Offline
Sparky,
You need to find the time-current curve for the device that you are using. The only one that I could find this morning for a 15 amp FRN-R fuse. It shows that this fuse will hold on average for 90 seconds at 20 amps, 30 seconds at 30 amps, and 2 seconds at 60 amps.
Other fuses and breakers will have different curves.
Re: What would you expect? #610 02/13/01 12:57 PM
I guess what I'm after are time current curves for:
FPE 2 pole 20 A
FPE 1 Pole 20 A (If it differs)
GE 2 Pole 20 A
SQD 2 Pole 20 A
If the hard data already exists, it will save me a lot of time. I've got the data from my own experiments, but I have a rather "noisy" lab.
I'll let you guys know what I found out, but I want to know your opinions (and any hard data you may know of) first.
You may be surprised!
[This message has been edited by sparky66wv (edited 02-13-2001).]
-Virgil
5 Star Inspections
Member IAEI
Re: What would you expect? #611 02/13/01 05:54 PM
Tom Offline
I looked at a curve for a SQ D 2 pole 50 & it shows a one minute trip at about 130%.
As Don pointed out, each breaker by each manufacturer will have it's own trip curve. You could probably contact UL to find out what they expect, but they would probably have to sell you the standard & they're usually expensive.
Re: What would you expect? #612 02/23/01 03:53 PM
In a nutshell... here are the results of my, uh..."tests"...
Single Pole 20A Breakers FPE on a 40A load to ground tripped between 38 and 74 seconds.
Double pole 20A Breakers FPE on a 40A load to ground tripped between 45 seconds and well over one minute (90+ sec). One breaker failed to trip after two minutes at 200% load. The 30 Amp SQ D Breaker upstream tripped instead, within 2 minutes at 150% load.
A SQ D 20A Breaker 2 Pole tripped within 20 seconds at 40A.
The 20 Amp breakers were the only ones I could test "safely". I had no idea it would take 200% to trip them in less than a couple of minutes. You should have seen me trying to find every high current device in the house to get these things to trip. Toasters, Coffee Pots, Blow Dryers, Heat Guns, Shop Vacs, etc. etc. Scared the cats...
I had it on two GFCI 20A receptacles. But even the #12 feeding them didn't get terribly warm, at double their "rated" current.
By the way, my wife is a nurse and is here when I do these crazy things... Wait 'til I get my Tesla Coil up and running!
-Virgil
5 Star Inspections
Member IAEI
Re: What would you expect? #613 02/23/01 08:53 PM
Tom Offline
'66
I'd like to be the first to congradulate you on getting any FPE breaker to trip under any condition. [Linked Image] I've met quite a few electricians who feel that an FPE breaker that trips out is in the realm of an urban legend.
[This message has been edited by Tom (edited 02-23-2001).]
Re: What would you expect? #614 02/23/01 09:59 PM
Bill Addiss Offline
'66
You must be in the Smoky Mountains?
(Joke)
Re: What would you expect? #615 07/01/01 07:46 AM
C.Urch Offline
I've cut live wires in two during remodels( by accident of course [Linked Image])frying my Kleins only to have a 20 Amp stab-lok breaker laugh in my face.
Re: What would you expect? #616 07/01/01 09:56 AM
Joe Tedesco Offline
Look here for more! www.stargroup.com
[This message has been edited by Joe Tedesco (edited 10-06-2001).]
Re: What would you expect? #617 07/01/01 10:19 AM
Joe Tedesco Offline
www.joetedesco.com
[This message has been edited by Joe Tedesco (edited 04-26-2003).]
2020 National Electrical Code
Code (NEC)
2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman
sbi
sbi
indiana
Show All Member Profiles
Admin 8
Trumpy 7
266,036 Are you busy
200,899 Re: Forum
189,556 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3