#6145 12/23/01 10:45 PM
Joined: Dec 2001
Posts: 37
A
aphares Offline OP
Member
In the 2002 NEC, There is now a definition in Article 240.2 of a tap conductor. Does this definition change the tap rule, or anyhting. Example: would you be able to set a trough out side a building or structure, install tapped conductors from there, and into six disconnects (rule), without a main?
Any thoughts.....Or am I just way off base?

Horizontal Ad
#6146 12/23/01 11:00 PM
Joined: Nov 2000
Posts: 2,148
R
Member
The definition was in 240-3(e) in the '99 code. There is no change in the application of the tap rules. The conductors in your example are not taps per the definition as they are service conductors. I see no problem with your example as long as the conductors leaving the trough have an ampacity at least equal to the OCPD installed in the disconnect. Of course the six disconencts would have to be grouped and nearset the point of entrance of the conductors.
Don(resqcapt19)


Don(resqcapt19)

Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
Radar
Radar
Los Angeles
Posts: 349
Joined: April 2004
Top Posters(30 Days)
Popular Topics(Views)
338,132 Are you busy
263,580 Re: Forum
243,616 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5