ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Shout Box
Recent Posts
High current GFI vs regular GFCI
by HotLine1. 11/15/18 02:32 PM
This anti-theist is priceless!!!
by djk. 11/14/18 07:19 AM
Single phase and what you call it.
by dsk. 11/12/18 11:10 AM
220/230/240V 60Hz Systems
by Albert. 11/07/18 12:48 AM
New in the Gallery:
What is this for?
Plug terminals
Who's Online Now
0 registered members (), 27 guests, and 30 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
arcing ground connection #61316
01/21/06 08:39 AM
01/21/06 08:39 AM
S
sandro2  Offline OP
Member
Joined: Mar 2005
Posts: 49
philadelphia,PA
I went to a house and at the cold waterpipe the ground was arcing against the water pipe.
I checked the neutral at the tap,meter socket and panel all were tight and made sure the neutrals and grounds were tight inside the panel. I tightened the ground connection and it stopped what could be the cause?

Work Gear for Electricians and the Trades
Re: arcing ground connection #61317
01/21/06 08:42 AM
01/21/06 08:42 AM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
The problem was a loose connection at the water pipe.

The 'cause' is required by the NEC.

The bonding of multiple services to a common underground water pipe results in current being carried on the water pipes.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: arcing ground connection #61318
01/21/06 09:22 AM
01/21/06 09:22 AM
S
sandro2  Offline OP
Member
Joined: Mar 2005
Posts: 49
philadelphia,PA
Thanks I just wanted to make sure I wasn't overlooking anything. I ran into this problem once before and it was a losse neutral at the taps along with alittle loose on the water pipe.

Re: arcing ground connection #61319
01/21/06 10:06 AM
01/21/06 10:06 AM
R
Rewired  Offline
Member
Joined: Jan 2006
Posts: 558
Hamilton, Ontario, Canada
I have seen grounds carry current even with the mains to the house open!
Sometimes your ground connection is a path for current should one of your neighbours say have a bad or open neutral somewhere in their service..
A.D

Re: arcing ground connection #61320
01/21/06 11:14 AM
01/21/06 11:14 AM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 7,038
Brick, NJ USA
Sandro:
A posibility also could be a 'bad' neutral connection on the utility side. Had that quite a few times, both OH & BUD.

John


John
Re: arcing ground connection #61321
01/21/06 06:16 PM
01/21/06 06:16 PM
L
LK  Offline
Member
Joined: Jan 2003
Posts: 1,429
New Jersey
Just came back from job plumber left and told homeowner to call electrician, we found loose neutral at service head, cut back. and cleaned, new bug, and we hope the plumber will return.

Re: arcing ground connection #61322
01/21/06 09:13 PM
01/21/06 09:13 PM
J
jdevlin  Offline
Member
Joined: Aug 2002
Posts: 402
welland ontario canada
Bad neutral at a neighboring property could be putting current onto the water pipe and back out your client's neutral.

Re: arcing ground connection #61323
01/22/06 02:24 PM
01/22/06 02:24 PM
W
winnie  Offline
Member
Joined: Sep 2003
Posts: 649
boston, ma
Check for a bad water heater element or another high resistance ground fault. A high resistance ground fault can cause significant current flow and power consumption, without tripping a breaker.

After you tighten the ground connection, it is worth putting a clamp meter on the GEC and flipping breakers to see if some particular circuit is causing the current flow.

-Jon


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
mxslick
mxslick
Atomic City, ID USA
Posts: 803
Joined: October 2004
Show All Member Profiles 
Top Posters(30 Days)
Admin 8
Popular Topics(Views)
251,487 Are you busy
188,678 Re: Forum
178,379 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.021s Queries: 14 (0.003s) Memory: 0.9926 MB (Peak: 1.1533 MB) Zlib enabled. Server Time: 2018-11-16 01:20:39 UTC