#61316 01/21/06 08:39 AM
Joined: Mar 2005
Posts: 49
S
sandro2 Offline OP
Member
I went to a house and at the cold waterpipe the ground was arcing against the water pipe.
I checked the neutral at the tap,meter socket and panel all were tight and made sure the neutrals and grounds were tight inside the panel. I tightened the ground connection and it stopped what could be the cause?

Horizontal Ad
#61317 01/21/06 08:42 AM
Joined: Jan 2003
Posts: 4,391
I
Moderator
The problem was a loose connection at the water pipe.

The 'cause' is required by the NEC.

The bonding of multiple services to a common underground water pipe results in current being carried on the water pipes.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
#61318 01/21/06 09:22 AM
Joined: Mar 2005
Posts: 49
S
sandro2 Offline OP
Member
Thanks I just wanted to make sure I wasn't overlooking anything. I ran into this problem once before and it was a losse neutral at the taps along with alittle loose on the water pipe.

#61319 01/21/06 10:06 AM
Joined: Jan 2006
Posts: 558
R
Member
I have seen grounds carry current even with the mains to the house open!
Sometimes your ground connection is a path for current should one of your neighbours say have a bad or open neutral somewhere in their service..
A.D

#61320 01/21/06 11:14 AM
Joined: Apr 2002
Posts: 7,413
Likes: 9
Member
Sandro:
A posibility also could be a 'bad' neutral connection on the utility side. Had that quite a few times, both OH & BUD.

John


John
#61321 01/21/06 06:16 PM
Joined: Jan 2003
Posts: 1,429
L
LK Offline
Member
Just came back from job plumber left and told homeowner to call electrician, we found loose neutral at service head, cut back. and cleaned, new bug, and we hope the plumber will return.

#61322 01/21/06 09:13 PM
Joined: Aug 2002
Posts: 402
J
Member
Bad neutral at a neighboring property could be putting current onto the water pipe and back out your client's neutral.

Horizontal Ad
#61323 01/22/06 02:24 PM
Joined: Sep 2003
Posts: 650
W
Member
Check for a bad water heater element or another high resistance ground fault. A high resistance ground fault can cause significant current flow and power consumption, without tripping a breaker.

After you tighten the ground connection, it is worth putting a clamp meter on the GEC and flipping breakers to see if some particular circuit is causing the current flow.

-Jon


Link Copied to Clipboard
Featured:

 Electrical
 Clearance

 *
 Tools
 *

 Books

 *

 Test Equipment

 

Advertisement:-Right
Member Spotlight
CharlieE
CharlieE
Indianapolis
Posts: 201
Joined: April 2004
Top Posters(30 Days)
davey 1
dsk 1
Popular Topics(Views)
554,729 Are you busy
428,936 Re: Forum
398,784 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5