#5938 12/15/01 10:10 AM
Joined: Dec 2001
Posts: 2
B
Junior Member
Does anyone know the underground depth required by NEC for branch line? It is about a 100' run to a pole building 100 amp service. 220v...? thanks

Joined: Aug 2001
Posts: 466
Likes: 1
J
Member
You would need to provide the following info: voltage, what is it being buried under, wiring method etc.

Joined: May 2001
Posts: 717
G
Member
Your burial depth does depend on if you're using conduit, or direct burial cable. The answer comes from Table 300-5. Assuming we are NOT going under a street, roadway, driveway but merely across a yard. Rigid conduit = 6", direct bury cable = 24", UF = 18". If your conditions are different, let us know.


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
The_Lightman
The_Lightman
Orlando, Fl, USA
Posts: 49
Joined: August 2001
Top Posters(30 Days)
Trumpy 9
NORCAL 5
Popular Topics(Views)
300,522 Are you busy
230,160 Re: Forum
214,976 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5