What are electricians using for fire alarms when pulling wires into slabs on grade or underground.Regular FAS cables are not approved for wet locatons. i have asked this question, and no one as been able to give me a definitive answer?
#59084 11/27/05 02:08 PM
Maybe you could pull through ENT
http://www.royalpipe.com/pdfs/ENT.pdf
#59085 11/27/05 02:39 PM
You can try asking a cable manufaturer. Here's a link to Belden's contact page. These guys also have a "cable college" on their site that's kind of interesting.
http://bwcecom.belden.com/sales/sal...efined&P5=undefined&P6=undefined
#59086 11/27/05 03:55 PM
You can run THWN conductors in PVC conduit. Be sure to identify the transition boxes somehow as FA.
We used to paint them red.
Earl
#59087 11/27/05 05:48 PM
Belden does make listed cable for such use. You'll have to dig around for it. It features a gel coating underneath the sheath and over the conductors.
However, I suspect you will find #14 THWN stranded much cheaper.
Your options are limited by the system spec's.