#58779 11/19/05 06:51 AM
Joined: Apr 2002
Posts: 7
H
Junior Member
if i run a 2/0 ground wire to the ground rod,how many ground rods do i install.do grnd rods have a specific size?mfg cannot answer this.i shouldnt have to run reststance tests untill i get enouge rods in. been too long. i used to know this.im getting too old i guess.rw

Horizontal Ad
#58780 11/19/05 07:23 AM
Joined: May 2002
Posts: 1,716
R
Member
Per the NEC, the rod must be a minimum of 5/8" in diameter, {250.52(A)(5)(b)}you would never need more than two rods and a #6 for the GEC.

If you are trying to meet a performance spec, you would need to install as many as it takes to get to the resistance number set by the spec and a larger conductor would help.

Roger

[This message has been edited by Roger (edited 11-19-2005).]


Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

Member Spotlight
BEAMEUP
BEAMEUP
WA
Posts: 27
Joined: December 2004
Top Posters(30 Days)
Admin 3
CSS 1
Popular Topics(Views)
366,297 Are you busy
289,265 Re: Forum
267,899 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5