Tripping main breaker #57196
10/07/05 05:15 AM
10/07/05 05:15 AM
P
poorboy  Offline OP
Member
Joined: Jun 2005
Posts: 124
Central Maine
I will be going to a job we did 2 yrs ago to investigate a problem that was explained to me by phone yesterday. I can't remember the precise specifics of this service but the general scope is this:

We installed a GE service with a high voltage switch (this is indoor and replaced an old transformer vault) with 4160 volts coming in, going thru a dry type transformer to a 208/120 section with a main breaker (can't remember the Amperage...prob 600 or 800 Amps).

When the "campus" electrical crew has shut down the 4160 on the site for various maintenance reasons and then restored power, the 208 volt main breaker in our installation tripped. I will be visiting the site soon and get the particulars on the type of breaker, whether it has any adjustments, etc.

Any thoughts on what I may be in for?

Work Gear for Electricians and the Trades
Re: Tripping main breaker #57197
10/07/05 05:57 AM
10/07/05 05:57 AM
P
pauluk  Offline
Member
Joined: Aug 2001
Posts: 7,520
Norfolk, England
It sounds as though it might be the combined surge currents of all the loads being re-energized simultaneously. Are there a good many motors for A/C compressors etc. on site?

I'd try opening some of the sub-feeder breakers, then turn on the power, then close the sub-feeds one at a time to minimize the surge currents.

Re: Tripping main breaker #57198
10/07/05 12:40 PM
10/07/05 12:40 PM
B
Bob  Offline
Member
Joined: Feb 2002
Posts: 182
Mobile, AL, USA
I agree with Paul. You did not say what the size of the transformer is. Also need to check the actual load. The transformer inrush plus the load pickup can be too great and trip the main breaker.

[This message has been edited by Bob (edited 10-07-2005).]

Re: Tripping main breaker #57199
10/07/05 01:09 PM
10/07/05 01:09 PM
I
IanR  Offline
Member
Joined: Dec 2004
Posts: 328
Palm Bay FL USA
I have to agree with Paul. It may be just that simple.(itemized power up) At my company we(not I, others I work with) have actually damaged panels and destroyed breakers because the power was restored to everything at once. Instead of gradually one item at a time. The inrush current at a system wide level can be staggering, say the least.

[This message has been edited by IanR (edited 10-07-2005).]

[This message has been edited by IanR (edited 10-07-2005).]

Re: Tripping main breaker #57200
10/07/05 03:41 PM
10/07/05 03:41 PM
P
poorboy  Offline OP
Member
Joined: Jun 2005
Posts: 124
Central Maine
Looked at it today...I was wrong, it is a fused switch, 1200 Amp GFI, the kind you have to pump the handle twice to turn on.(high pressure contact switch) The rep I called is looking at the job file to see if it has been programmed (or calibrated?) properly. They will have a record of it if it was. I was not involved if it was, but will report back what I find out. Must be related to this feature, as the load is nowhere near 1200 Amps and there is very little motor load. It has no transformers on the load side of it, just the one for 4160 to 208 which feeds it.

[This message has been edited by poorboy (edited 10-07-2005).]

Re: Tripping main breaker #57201
10/07/05 04:48 PM
10/07/05 04:48 PM
C
CTwireman  Offline
Member
Joined: Feb 2002
Posts: 840
Connecticut, USA
I "third" the inrush current motion.


Peter
Re: Tripping main breaker #57202
10/07/05 09:58 PM
10/07/05 09:58 PM
R
rj  Offline
Member
Joined: Jan 2003
Posts: 21
Skidmore, Missouri, USA
Kind of sounds like a problem I got called back to work for this week. They lost power to a building. It was a 1200 amp GFI main that tripped. I turned off all the breakers in the dist. panel and reset it. I turned the breakers on one at a time but when I came to a 350 amp. breaker, boom the main would trip. Come to find out we had a bad contactor for a motor.
Do they just reset the main or do they shut all sub panels off and bring them on one a time? That could be a problem if they just reset the main and try to start everything up all at once.

Re: Tripping main breaker #57203
10/08/05 07:54 AM
10/08/05 07:54 AM
P
poorboy  Offline OP
Member
Joined: Jun 2005
Posts: 124
Central Maine
I am handicapped here by not knowing yet what the "programming" that was/wasn't done to the switch is all about. If it is supposed to have been done in response to a detailed load survey and things have changed in the 2 yrs since, then reprogramming may be in order. I am covering for people (who were involved in this job) who were out of town for a week when this call came in. They will know if the initial start up was done per spec. I am eager to learn more about that aspect of it, and at the same time open to the possibility of the inrush theory,too.

Always good to be challenged by these things, and its also good to have a large cross section of electricians to run it by. Thanks, and I'll keep you posted.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Admin
Admin
NY, USA
Posts: 3,481
Joined: October 2000
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 16
Potseal 15
Popular Topics(Views)
243,586 Are you busy
180,381 Re: Forum
170,859 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.018s Queries: 14 (0.004s) Memory: 0.9930 MB (Peak: 1.1516 MB) Zlib enabled. Server Time: 2018-01-22 00:27:06 UTC