fluorescent watts #56356
09/19/05 07:47 PM
09/19/05 07:47 PM
K
kd  Offline OP
Member
Joined: Dec 2004
Posts: 52
Does the 32 watt rating of a fluorescent tube include the electricity used by the ballust?

Work Gear for Electricians and the Trades
Re: fluorescent watts #56357
09/19/05 07:50 PM
09/19/05 07:50 PM
A
Active 1  Offline
Member
Joined: Feb 2003
Posts: 687
Grayslake IL, USA
No

Re: fluorescent watts #56358
09/19/05 09:01 PM
09/19/05 09:01 PM
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
More to the point, the watt rating of the bulb is nominal, not actual. The actual electricity used by the complete fixture is indicated by the current marking on the ballest itself.

Re: fluorescent watts #56359
09/19/05 10:18 PM
09/19/05 10:18 PM
S
ShockMe77  Offline
Member
Joined: Jun 2005
Posts: 821
Rahway, New Jersey
This topic is something I did not know for the longest time. It's very important for calculating loads for several fluorescent light on the same circuit. And until rcently, I would always mispell FLUORESCENT.

Re: fluorescent watts #56360
12/23/05 10:47 PM
12/23/05 10:47 PM
R
RODALCO  Offline
Member
Joined: Dec 2005
Posts: 856
Titirangi, Akld, New Zealand
Add at least 30% for choke on top of wattage rating of tube.


The product of rotation, excitation and flux produces electricty.
Re: fluorescent watts #56361
12/24/05 05:38 AM
12/24/05 05:38 AM
Scott35  Offline

Broom Pusher and
Member
Joined: Oct 2000
Posts: 2,708
Anaheim, CA. USA
Fluorescent Lamps will almost always consume less wattage than the listed rating shows.

For example, an F32T8 Lamp draws a nominal 29 watts, and the most it will ever draw will be 31 watts.

Lamps using Rapid Start (Hot Cathode) operation will have wattages drawn by both the heating of the cathodes, and the transduction of Electron emission / inert material bombardment, into visible light output.

The True Power drawn for heating of the cathodes is "parasitic", as viewed to overall output light vs. input wattage. It does not directly transduce into visible light output, only helps make the emission of Electrons more efficient.

Ballast load consumption of True Power is also "parasitic", as it does not produce any visible light at the lamp.

Whatever heat is felt at the Ballast is the resultant of the True Power it has consumed from the Generating Source.

Typicals for a 2 lamp Magnetic Ballast, driving two F40T12 Lamps, were like 4 watts consumed by the ballast - and around 77 watts by the lamps - with an additional 2 watts
drawn to heat the Lamps' cathodes.

***NOTE***

Do not confuse input (Line) Volt-Amperes with input wattage

Linear Reactor Core Ballasts will normally draw around 1.25 times the rated lamp wattage, as input VA.
This would equal what would be seen on an ammeter measuring the input to the Ballast -
vs.
the input system voltage -
so there is an obvious Power Factor Scenario here [Linked Image]

For the "Non-Magnetic" flavors of Ballastry currently being used

Depending on the designed functions of Electronic & Hybrid type Ballastry, some may drive lamps at high power levels, some at low power levels (a lot of the ones I deal with drive lamps at the lower power levels), and others will drive lamps at the "best for the current conditions" power level.

Also, these Ballasts may have a Leading Power Factor, Lagging Power Factor, or the mind boggling
"Almost as close to unity Power Factor as a pure Resistance Load would be - yet still be a Reactive Load"

Again, whatever heat is felt at the ballast, will represent a large portion of the wattage drawn from the generating source by it (drawn by the ballast).

BTW: The "Generating Source" might be:
  • Steam Power Prime Mover, using Coal as Fuel,
  • Steam Power Prime Mover, using Oil as Fuel,
  • Steam Power Prime Mover, using Uranium 235 as Fuel (via reactor core and moderator),
  • Steam Power Prime Mover, using Geothermic Energy (or the Earth as Fuel),
  • Internal Combustion Engine Prime Mover, using Gasoline or Diesel as Fuel,
  • Gas Turbine Prime Mover, using Natural Gas as Fuel,
  • Pedal Powered / Human Being Prime Mover, using Carbohydrates (food) as Fuel.


Scott35

edited to courrekt spel-lieenng miss steaks

[This message has been edited by Scott35 (edited 12-24-2005).]


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Re: fluorescent watts #56362
12/24/05 07:30 AM
12/24/05 07:30 AM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Code wise there is this.

Quote
210.4(B) Inductive Lighting Loads.

For circuits supplying lighting units that have ballasts, transformers, or autotransformers, the computed load shall be based on the total ampere ratings of such units and not on the total watts of the lamps.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: fluorescent watts #56363
12/24/05 12:24 PM
12/24/05 12:24 PM
P
pauluk  Offline
Member
Joined: Aug 2001
Posts: 7,520
Norfolk, England
Over here, there was a long-standing rule that in the absence of more detailed information and specific p.f. correction the VA rating for calculating current demand must be taken as the lamp rating in watts multiplied by at least 1.8.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
The_Lightman
The_Lightman
Orlando, Fl, USA
Posts: 49
Joined: August 2001
Show All Member Profiles 
Top Posters(30 Days)
sparky 11
Popular Topics(Views)
250,380 Are you busy
187,991 Re: Forum
177,541 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.027s Queries: 14 (0.005s) Memory: 0.9960 MB (Peak: 1.1559 MB) Zlib enabled. Server Time: 2018-10-18 09:26:58 UTC