ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

>> Home   >> Electrical-Photos   >> Classifieds   >> Subscribe to Newsletter   >> Store  
 

Photo of the Week:

Old POCO Letter
Old POCO Letter

Advertisement:-Left
Recent Gallery Topics:
What in Tarnation?
What in Tarnation?
by timmp, September 10
Plumber meets Electrician
Plumber meets Electrician
by timmp, September 10
Who's Online Now
0 members (), 48 guests, and 15 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 1 of 2 1 2
#56217 09/17/05 01:46 AM
Joined: Mar 2003
Posts: 9
S
Member
Is it code to use armored cable in a barn, and use plastic junction boxes? Its all open wall and ceiling,I was going to use the 12-3 armored for all the runs split the 12-3 for the lights and outlets then use two breakers for that whole run.

Horizontal Ad
Joined: Jan 2003
Posts: 4,391
I
Moderator
As you said barn it may well be an agricultural building per 547.1(A) and (B).

If it is an agricultural building steel jacketed AC cable is out of the question.

Also and more importantly, plastic boxes with steel cables and raceways are a very bad idea.

At the least you should read Article 547.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Joined: Nov 2002
Posts: 456
C
Member
Where I am at (Ontario Canada), standard practice in older wooden/open frame agricultrural buildings is NMW-10 cable (AKA UF-B), and surface mount bakelite fittings. New er "closed frame" barns will have PVC conduit and fittings. The service panel is either in a "doghouse" on the outside of the barn, or in an anteroom or mechancial room sealed from where the livestock is kept.

Joined: Mar 2003
Posts: 29
M
Member
If this is an agricultural building as described in 547.1(A) or (B), MC cable would be allowable but definitely not AC. And if MC cable were used, plastic boxes would have to meet the exceptions to 314.3, otherwise they are not permitted with metal raceways or metal-armored cables.

Joined: Jan 2003
Posts: 4,391
I
Moderator
That MC would have to have a plastic jacket as well.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Joined: Mar 2003
Posts: 9
S
Member
This barn is all wood has two horses in there own stalls, used for horses only big sliding doors, armored cable is my first choice. I dont want any rats chewing wire, is this ok? I will be in Riverside county, Ca for this job. This is the best forum for questions and answers, something you can't get at Barns and Noble book store.

Joined: Jan 2003
Posts: 4,391
I
Moderator
No typical armored cable is not OK.

The only armored cable allowed would be jacketed MC cable which looks like prewired liguidtight. It is not cheap.

UF cable (looks like NM) is OK but I would go with PVC conduit with PVC boxes.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Horizontal Ad
Joined: Mar 2003
Posts: 9
S
Member
Ok, looks like pvc with plastic boxes will do, the concern was stories I read about barn fires caused from metal boxes rusted from moisture with changing temperture's and animal waste the acid's speeding up the decay on metals, That would be great if there was a spray coating that could protect the armored cable like a rust proof application.
Now one point I wanted to make was the armored cable if out of reach like the ceiling runs, would that exception be possible? Ok Ok OK the secrect is out. I love armored cable, but I love horses also I want to be the safest first!

Joined: Jul 2004
Posts: 10,004
Likes: 36
G
Member
Whats wrong with regular aluminum MC? It is wet location listed according to the box. I can see a grounding issue with plastic boxes if the connector doesn't have a bonding lug.


Greg Fretwell
Joined: Jan 2003
Posts: 4,391
I
Moderator
Nothing, except it is not allowed by 547.5(A)

Quote
547.5 Wiring Methods.
(A) Wiring Systems. Types UF, NMC, copper SE cables, jacketed Type MC cable, rigid nonmetallic conduit, liquidtight flexible nonmetallic conduit, or other cables or raceways suitable for the location, with approved termination fittings, shall be the wiring methods employed. Article 398 and Article 502 wiring methods shall be permitted for areas described in 547.1(A).


I believe corrosion is the issue, notice only copper SE cable is allowed.

Notice the absence of RMC and FMC from the list.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Page 1 of 2 1 2

Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
Posts: 362
Joined: April 2003
Top Posters(30 Days)
dsk 1
Popular Topics(Views)
337,240 Are you busy
262,772 Re: Forum
243,070 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5