0 members (), 262 guests, and 15 robots.
Page 1 of 4 1 2 3 4
#56121 09/15/05 08:52 PM
bot540 Offline OP
I know this has probally been asked a thousand times but does the neutral in a 2 wire single phase circuit(ie: a small apliance branch circuit) count as a current carrying conductor?
Jesus may have been a capenter,but God was an electrician.Genesis1:3
You don't have a neutral in a two wire circuit. [Linked Image]
You have a ungrounded conductor, a grounded conductor and maybe a grounding conductor.
Both the ungrounded conductor and grounded conductor are current carrying conductors.
Bob
Absolutely, in a 2 wire circuit it is impossible to have a neutral conductor. Click Here
Roger
I was a little slow on that one Bob. [Linked Image]
Roger
bot540 Offline OP
Thanks guys I just read the post in the nec forum and understand.
...Bob,I may be wrong here,but,isn't the grounded conductor considered current-carrying ONLY when used in circuits where there are non-linear loads harmonics,such as HID lighting,servo controls,ballasts,or in a 3 phase wye utilizing only 2 phases and a neutral...etc??otherwise,if the circuit is balanced,the current on the neutral is 0,you wouldn't count it as current -carrying for derating purposes,ampacity..??
Russ
Attic Rat, the OP was asking about a two wire circuit, not a multiwire circuit where current could balance in the neutral.
-Jon
Ooops,..my bad... [Linked Image] [Linked Image]
bot540 Offline OP
Does a grounded conductor have to be perfectly balanced in order not to be counted as a current carrying conductor? Can someone give a feild example?
... Take a normal 3 phase wye circuit,..all sharing the neutral,and the loads close to being equal...(barring the use of HID fixtures,processors,variable speed drives etc)and you should have a balanced circuit..
Russ
Page 1 of 4 1 2 3 4