Ungrounded Delta Service #56043
09/13/05 07:44 AM
09/13/05 07:44 AM
F
Frank Cinker  Offline OP
Member
Joined: Jul 2001
Posts: 311
Pennsylvania
In several of our local government buildings we have a 230V, 3Ph, 3W. electrical service. Measuring voltage to ground; A-G=230 volts, B-G=230 volts, C-G=0 volts. Why isn't there any voltage to ground on one phase?

[This message has been edited by Frank Cinker (edited 09-13-2005).]

Work Gear for Electricians and the Trades
Re: Ungrounded Delta Service #56044
09/13/05 07:47 AM
09/13/05 07:47 AM
W
winnie  Offline
Member
Joined: Sep 2003
Posts: 649
boston, ma
Phase C is grounded. If this is supposed to be an ungrounded service, then there is a fault somewhere. But this is very likely 'corner grounded' delta rather than 'ungrounded' delta.

-Jon

Re: Ungrounded Delta Service #56045
09/13/05 08:53 AM
09/13/05 08:53 AM
H
HighPotter  Offline
Member
Joined: Aug 2004
Posts: 42
So. Cal
Ungrounded systems are common in powerplants or substations. That way, IF one phase does become grounded, life goes on. Control of operations isn't effected.
Now a ground on a 2nd phase is another thing.

But I agree with Winnie. You most likely have a corner grounded system.If that is the case, your phase to ground reading is irrelevant.

HP

Re: Ungrounded Delta Service #56046
09/13/05 11:21 AM
09/13/05 11:21 AM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,298
Estero,Fl,usa
That conductor should be white.


Greg Fretwell
Re: Ungrounded Delta Service #56047
09/13/05 10:51 PM
09/13/05 10:51 PM
L
Larry Fine  Offline
Member
Joined: Feb 2005
Posts: 693
Richmond, VA
You're so prejudiced!


Larry Fine
Fine Electric Co.
fineelectricco.com
Re: Ungrounded Delta Service #56048
09/13/05 11:36 PM
09/13/05 11:36 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,298
Estero,Fl,usa
The jokes just write themselves from there don't they.


Greg Fretwell
Re: Ungrounded Delta Service #56049
09/15/05 12:14 AM
09/15/05 12:14 AM
W
wolfdog  Offline
Member
Joined: Oct 2001
Posts: 135
Dallas,TX
I occasionally run into corner grounded delta in this area. It is rare and I have never gotten a good explanation for why that configuration appears in just one building in a neighborhood.
It seems to be old installations.

Anybody got a definitve answer?

Re: Ungrounded Delta Service #56050
09/15/05 01:07 AM
09/15/05 01:07 AM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,298
Estero,Fl,usa
It is a very clean way to install 3p delta for motor loads if you don't need to serve 120v loads. You can use 2 pole equipment, one fewer service conductor and have 240v to run your motor on vs the 208 you get with wye.
Do you like "red leg" better? That comes with it's share of confusion too.


Greg Fretwell
Re: Ungrounded Delta Service #56051
09/15/05 09:08 AM
09/15/05 09:08 AM
W
wolfdog  Offline
Member
Joined: Oct 2001
Posts: 135
Dallas,TX
240 with a high leg is very common in this area.

Two of the 240 corner grounded delta have been on an elementary school and a private school that was formerly an orphanage. Both had small a\c loads - split systems and small rooftops -no chillers. Both systems served lights and receptacles.
3 pole main disconnect with a solid plug in the grounded phase. 3 wires in and 3 wires out.

Re: Ungrounded Delta Service #56052
09/15/05 09:10 AM
09/15/05 09:10 AM
R
Ryan_J  Offline
Moderator
Joined: Aug 2003
Posts: 1,374
West Jordan, Utah, USA
I think if this were an ungrounded system your measurement from phase "A" to ground and from phase "B" to ground would not be that close to each other. With an ungrounded system, the phase voltage to ground is erratic.


Ryan Jackson,
Salt Lake City
Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
waymag
waymag
dallas, texas, USA
Posts: 68
Joined: January 2002
Show All Member Profiles 
Top Posters(30 Days)
sparky 11
Admin 7
Popular Topics(Views)
250,663 Are you busy
188,143 Re: Forum
177,831 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.024s Queries: 15 (0.004s) Memory: 1.0242 MB (Peak: 1.2001 MB) Zlib enabled. Server Time: 2018-10-23 16:14:22 UTC