#55967 09/10/05 07:55 PM
Joined: May 2001
Posts: 378
F
frank Offline OP
Member
Is it ok to leave stored energy breaker in the charged position?We had a power factor correction cap catch fire on an Mcc and when i went to close the distrobution breaker i found that it was aready charged and must have been that way since Seimans racked it months ago?personaly i always leave them discharged once closed.
thanks

Horizontal Ad
#55968 09/10/05 08:17 PM
Joined: Aug 2001
Posts: 599
N
Member
I can't say if it's good or bad but insulated case breakers with motor operators recharge themselves right after they close by design. The springs stay charged until the breaker needs to close again.

#55969 09/16/05 01:24 PM
Joined: Sep 2005
Posts: 120
Z
Zog Offline
Member
Drawout circuit breakers with charging motors should have a spring discharge interlock so the closing springs are discharged automaticly when they are racked out. I dont see any other hazard of leaving the springs charged.


MV/HV Testing Specialist, "BKRMAN"
#55970 09/16/05 05:32 PM
Joined: Jan 2005
Posts: 155
D
Member
After a breaker is closed the "spring" can be recharged without a problem. A breaker will always trip no matter if you have charged the spring or not. If you choose to recharge the spring after closing the breaker the beaker can be tripped, reclosed, and tripped again. After that you have to recharge the spring to close the breaker again.
A motor operator will always keep the spring charged instead of you doing it manually.
Bottom line is don't worry about it and simply keep the spring recharged as most commonly do.

#55971 09/18/05 08:47 PM
Joined: Mar 2004
Posts: 391
B
Member
Can any of ya'll provide me with a quick description or a link to a comprehensive source that describes what "stored energy breakers" are? I've never heard of them before but from what I read here I have a suspicion they might be similar to those large breakers in switchgear cabinets that have to be "pumped" several times before they can be closed. Is that close?

Thanks.

-John

#55972 09/19/05 10:16 AM
Joined: May 2001
Posts: 378
F
frank Offline OP
Member
BigJohn,yes we are talking about the same device exactly.I'm not 100% sure I'm calling it by the right name either so...
Dave T,I imagine if the breaker is left charged and then discharged while already closed it's not a problem?It just seems that there is less confusion if its discharged.
In this instance the the open/close flag had spun past the veiwing window so you could see inside the breaker as well.

[This message has been edited by frank (edited 09-19-2005).]

#55973 09/19/05 11:42 AM
Joined: Sep 2005
Posts: 120
Z
Zog Offline
Member
The correct terminology would be a drawout low voltage power circuit breaker with a motor charged-spring operated mechinism.


MV/HV Testing Specialist, "BKRMAN"
Horizontal Ad
#55974 09/19/05 12:08 PM
Joined: Jan 2005
Posts: 155
D
Member
Because these breaker require such high energy springs to close the contacts you would have a manual charging handle that must be operated numerous times in a ratcheting movement, pumped, to charge the spring. It can not be done in one motion like would be cone with a common industrial breaker. I don't know how many out there have had the privilege of closing a 2500a frame industrial molded case circuit breaker but it's very difficult if you don't have that handle extension installed.
So on both LV power and MV breakers they are designed such that you use a ratcheting movement to wind the spring then close the breaker with a simple push of a button.
These breakers can be closed electrically with a spring release solenoid and opened remotely with a shunt trip. The motor operated is added to recharge the spring when it discharges so that you don’t have to.


Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
Posts: 362
Joined: April 2003
Top Posters(30 Days)
Popular Topics(Views)
347,110 Are you busy
272,221 Re: Forum
252,578 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5