Distance from sprinkler heads? #55739
09/04/05 11:28 PM
09/04/05 11:28 PM
B
bot540  Offline OP
Member
Joined: Sep 2004
Posts: 174
Vernon Hills, IL
What is the minimum distance allowed for lights, smoke detectors, ect. from sprinkler heads?


Jesus may have been a capenter,but God was an electrician.Genesis1:3
Work Gear for Electricians and the Trades
Re: Distance from sprinkler heads? #55740
09/04/05 11:53 PM
09/04/05 11:53 PM
U
u2slow  Offline
Member
Joined: Sep 2003
Posts: 200
Salt Spring, BC, Canada
IIRC thats a Building Code issue... I think the last job I was on that we had issues, the inspector wanted to see 12" minumum to the edge of the fixture.

Re: Distance from sprinkler heads? #55741
09/05/05 01:47 AM
09/05/05 01:47 AM
G
georgestolz  Offline
Member
Joined: Jun 2005
Posts: 91
Fort Collins, CO, US
Check out this thread .

I think the rule of thumb is 3 times the size of the obstruction--so a mushroom five inches deep would need to be fifteen inches from the head. [Linked Image]


-George
Re: Distance from sprinkler heads? #55742
09/06/05 12:41 PM
09/06/05 12:41 PM
G
George Corron  Offline
Member
Joined: May 2001
Posts: 717
Lorton, Va USA
If you can lay your hands on an NFPA-13, you will find your answer in there. No violation on a flush fixture (should not be touching though), and basically the 3X rule is correct except that your need to use the dimension which gives you the greater rating of depth or width.

You will find your dead on answer in NFPA-13, chapter 8, section 8.7

I know that's confusing, but it depends on exactly what you have there. I was looking up the answer for you when my FPE looks over my shoulder, and he came up with the same answer, so maybe for once both of us are right.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
SafetyWired
SafetyWired
Pa, USA
Posts: 44
Joined: July 2013
Show All Member Profiles 
Top Posters(30 Days)
Admin 5
Popular Topics(Views)
248,158 Are you busy
185,629 Re: Forum
174,991 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.019s Queries: 14 (0.004s) Memory: 0.9592 MB (Peak: 1.0926 MB) Zlib enabled. Server Time: 2018-07-22 06:55:51 UTC