Metal clad , Armored clad ? #55315
08/25/05 02:16 PM
08/25/05 02:16 PM
D
drgnz23  Offline OP
Member
Joined: Feb 2002
Posts: 56
los angeles
Whats the difference and can you use it in a hospital enviroment in southern california

Work Gear for Electricians and the Trades
Re: Metal clad , Armored clad ? #55316
08/25/05 05:07 PM
08/25/05 05:07 PM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
The difference that counts is the armor jacket of AC cable is a grounding conductor.

The armor of MC cable is generally not a grounding conductor.

If your working in an area that requires redundant grounding you will need to use hospital grade AC cable.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: Metal clad , Armored clad ? #55317
08/25/05 07:08 PM
08/25/05 07:08 PM
F
frank  Offline
Member
Joined: May 2001
Posts: 376
windsor ontario canada
iwire,What is hospital grade AC.I'm a canuck so we may not have it here or if we do it's not required.We use just regular ac90.We do use ISO ac90 which has both an insulated ground and bare ground in our LIM panels.

Re: Metal clad , Armored clad ? #55318
08/25/05 08:18 PM
08/25/05 08:18 PM
D
distributor x  Offline
Member
Joined: Jul 2005
Posts: 57
Canada

Re: Metal clad , Armored clad ? #55319
08/26/05 12:51 PM
08/26/05 12:51 PM
D
drgnz23  Offline OP
Member
Joined: Feb 2002
Posts: 56
los angeles
517.13 (a) All branch circuits serving patient areas shall be provided with a ground path for fault current by installation in a metal raceway system, or a cable having metallic armor or sheath assembly.
Am i reading this wrong

Re: Metal clad , Armored clad ? #55320
08/26/05 12:59 PM
08/26/05 12:59 PM
C
CTwireman  Offline
Member
Joined: Feb 2002
Posts: 840
Connecticut, USA
drgnz23,

As Bob said, you must use Type HCF cable. This is a form of AC cable, colored green to indicate that it's HCF.

HCF is constructed to include an insulated grounding conductor to meet this requirement. As with all AC cable, the armor is suitable for grounding.


Peter
Re: Metal clad , Armored clad ? #55321
08/26/05 01:33 PM
08/26/05 01:33 PM
R
Roger  Offline
Member
Joined: May 2002
Posts: 1,716
N.C.
drgnz23, you are reading 517.13(A) correctly. The metallic raceway or cable sheath shall itself be a ground path for fault current and there shall also be a wire conductor ground path for fault current.

HCF or HCFC meets this requirement.

Check out this link.
http://www.afcweb.com/table2_.html

Now, depending on what code cycle you are dealing with, you may or may not be allowed to use this wiring method for the "Emergency System" wiring.

Roger

[This message has been edited by Roger (edited 08-26-2005).]

Re: Metal clad , Armored clad ? #55322
08/26/05 06:37 PM
08/26/05 06:37 PM
S
SolarPowered  Offline
Member
Joined: Jul 2004
Posts: 625
Palo Alto, CA, USA
I'm curious about how exactly this works--what do you do with the two grounds? I'm guessing that the armor ground is used to ground the box, and the insulated ground is for an isolated ground on the receptacle itself?

I don't understand what the rational is for the two grounds. If someone could explain what advantages they are supposed to bring, I would love to understand this.

Thanks!

Re: Metal clad , Armored clad ? #55323
08/26/05 07:13 PM
08/26/05 07:13 PM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
No the 'extra' is not for isolated grounding.

It is simply for redundancy.

Call it a 'back up ground'. [Linked Image]


Bob Badger
Construction & Maintenance Electrician
Massachusetts

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
TOOL_5150
TOOL_5150
Bay Area
Posts: 61
Joined: August 2007
Show All Member Profiles 
Top Posters(30 Days)
Admin 7
Popular Topics(Views)
251,638 Are you busy
188,766 Re: Forum
178,483 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.024s Queries: 14 (0.005s) Memory: 1.0011 MB (Peak: 1.1703 MB) Zlib enabled. Server Time: 2018-11-20 16:07:15 UTC