#55257 08/23/05 03:02 PM
Joined: Jan 2005
Posts: 61
J
jkochan Offline OP
Member
Can anyone give me a reason why an Open Air-Over couldn't me used in place of a TEAO in the following application? This is a CanCoil condensing unit for an AirFlow AFX2000 series computer room type ac unit. The condensing unit is roof mounted, non-explosive environment in Phoenix AZ. It's a three Phase 460/380 1/2 hp, 1140 rpm, 56 frame, non-inverter duty. I can find all kinds of OAO's but have to order a TEAO from either GE or CANCOIL at considerable expense. It seems to me that the OAO would have better cooling in our environment. I prefer OEM where possible but these motors are not stocked locally and everyone who lists it must order it in. Shipping costs on a motor almost pays for a second OAO available locally

#55258 08/23/05 04:36 PM
Joined: Jan 2003
Posts: 4,391
I
Moderator
Rain?


Bob Badger
Construction & Maintenance Electrician
Massachusetts
#55259 08/24/05 10:31 AM
Joined: Jan 2005
Posts: 61
J
jkochan Offline OP
Member
Over 1/2 the motors I see on AC out here are open types, ususally with rain shields if mounted shaft up. These are also usually 1 phase motors. Any reason a 3 Phase should be any different? Higher voltage maybe?

#55260 08/24/05 02:09 PM
Joined: Apr 2004
Posts: 156
R
Member
TEAO's keep out rain dust and droppings and the majority of condenser fans are mounted shaft up with wire grills over them.

Have you looked into Baldor motors? They may have a motor that can replace yours if the mount and blade will work with it.


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Alan Belson
Alan Belson
Mayenne N. France
Posts: 1,803
Joined: March 2005
Top Posters(30 Days)
triple 3
BigB 3
Popular Topics(Views)
303,157 Are you busy
232,169 Re: Forum
216,902 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5