I was asked this today due to a wrong spec on a job. The shade company required a 12-2 romex at each window shade location for power, so I did it. I went there today to start the install and reading the shade info it needs a 12-3 romex to work. The shade guy wants to use the ground conductor as a neutral and I told him no way no how. I am just thinking now though what is the real reason behind this. Safty because no ground? The current on the neutral now is not insulated on it's return trip?
|
|
|
|
|
Joined: May 2003
Posts: 2,876
Member
|
"Safty because no ground? The current on the neutral now is not insulated on it's return trip?"
YES And YES (Could also cause ground / neutral contact in a metalic box - after the main.)
Mark Heller "Well - I oughta....." -Jackie Gleason
|
|
|
|
|
Joined: May 2003
Posts: 2,876
Member
|
Oh, been in this situation before...
If its you fault... Look into romote control ones, cheaper than re-finish sometimes.
Not your fault, T&M C/O!
Mark Heller "Well - I oughta....." -Jackie Gleason
|
|
|
|
|
Joined: Apr 2002
Posts: 7,413 Likes: 10
Member
|
OK, the bare conductor will be carrying the current as you said, and basically be "live" to a grounded object, box, etc; or a person.
YES it is a saftey issue, yes, it is NOT NEC compliant, and yes you are 100% right saying 'no way'.
I have seen instances where EMT was used as the 'neutral' for a 30 amp, 120 volt circuit that consisted of ONE 'hot' conductor. Yes, it worked, but the setscrew couplings were not tightened properly and started arcing. It almost caused a fire, as the EMT was installed on a wall that had clothing racks mounted on it.
Some of the 'old timers' used to say "gyp the ground" when you had a 'open' neutral to restore the circuit; heck I saw BX armour that was 'live' arcing on suspended ceiling grid.
You're right; illegal, unsafe, and not to be done.
John
John
|
|
|
|
|
Joined: Jun 2005
Posts: 821
Member
|
Oh, what the heck, as long as it works, right?
*rollseyes
What "electrician" walks away from a job thinking it's ok to use EMT as the grounded conductor?
|
|
|
|
|
Joined: Oct 2004
Posts: 265
Member
|
Er, misread something
[This message has been edited by dmattox (edited 07-29-2005).]
|
|
|
|
|
Joined: Oct 2003
Posts: 259
OP
Member
|
I know not to do it and will get paid to fix it. The shade system is part of a larger system that is all tied together for controlling lighting, video and sound systems so doing anything but snaking in new cables will not work.
|
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
I know not to do it and will get paid to fix it. Good choice. ![[Linked Image]](https://www.electrical-contractor.net/ubb/smile.gif) Do not listen to "The Shade Guy" he is not NEC trained and he is not on the hook if the electrical portion of the shades causes a problem. Would you tell him how to hang drapes?
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
|
Joined: Oct 2000
Posts: 2,749
Member
|
Because, 334.108 Equipment Grounding.
In addition to the insulated conductors, the cable shall have an insulated or bare conductor for equipment grounding purposes only.
Joe Tedesco, NEC Consultant
|
|
|
|
|
Joined: Oct 2003
Posts: 259
OP
Member
|
Thanks guys. I know not to do it just wanted to make sure I was right in my reasons, besides the code.
|
|
|