ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
Recent Posts
Casino Wiring methods
by HotLine1. 12/09/17 10:44 AM
Ground wire Size to water Line.
by HotLine1. 12/05/17 12:11 PM
Flexible conduit to an outside Spa
by gfretwell. 12/05/17 12:28 AM
2017 NEC Changes
by luckyshadow. 12/04/17 06:08 PM
Dimmable LED 2x4 lay in fixtures
by Vulsion. 11/30/17 06:37 PM
New in the Gallery:
Gallery Test
Popular Topics(Views)
242,991 Are you busy
179,385 Re: Forum
170,352 Need opinion
Who's Online Now
0 registered members (), 14 guests, and 9 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#54425 - 07/28/05 10:59 PM bonding panels in multi family homes  
Joey D  Offline
Member
Joined: Oct 2003
Posts: 259
Arlington MA U.S.
It's way past my bed time so maybe thats why I don't see this in the book.
I have a 2 family house and i ran my ground to the meter socket, 2 gang and did not jump the panels together with an additional bonding conductor. I never go to the meter socket and just jump the panels together but this time I did it differently and the inspector picked up on it.


Work Gear for Electricians and the Trades

#54426 - 07/30/05 05:32 AM Re: bonding panels in multi family homes  
poorboy  Offline
Member
Joined: Jun 2005
Posts: 124
Central Maine
What's the setup? Main breakers in the meter trim and 4 wires to each panel, or meter trims only and 3 wires directly into the 2 panels via the shortest route? My ground rods always go to the meter trims on residential services, and the cold water to the panel, which is usually a main breaker panel. What was the inspector's specific objection?


#54427 - 07/30/05 05:21 PM Re: bonding panels in multi family homes  
Joey D  Offline
Member
Joined: Oct 2003
Posts: 259
Arlington MA U.S.
It's a resi 3 gang meter socket with just SEU into the 3 panels. I went from the meter to the 1st rod then to the water and the second rod, #4 copper.
His response was the panels are next to each other so they need to be bonded together. I would think they were bonded together thru the bar in the meter socket.


#54428 - 07/30/05 05:26 PM Re: bonding panels in multi family homes  
Joey D  Offline
Member
Joined: Oct 2003
Posts: 259
Arlington MA U.S.
408.40 is what he showed me.


#54429 - 07/30/05 06:46 PM Re: bonding panels in multi family homes  
Electricmanscott  Offline
Member
Joined: Jan 2002
Posts: 1,457
Holden, MA USA
Joey, 404.28 does not have anything to do with the grounding electrode connection to the service. That is the requirement for grounding the cabinet itself and the connection of the equipment grounds that terminate within that panel. You need to look at 250.24 specifically A 1 That says The grounding electrode conductor "connection can be made at any accesible point from the load end of the service drop or lateral to and including the terminal or bus to which the grounded service conductor is connected at the service disconnecting means."
This to me says the gec can terminate at any place on the line side of the service you wish.
Mike Holts book seems to confirm what I say here. He says the connection can be made at the service drop, the meter, or the disconnecting means.
Like you I'd like to see some other thoughts on this. Either way I think your inspector is barking up the wrong tree citing 404.40.

Feel free to name the town.

[This message has been edited by Electricmanscott (edited 07-30-2005).]


#54430 - 07/31/05 09:13 PM Re: bonding panels in multi family homes  
Joey D  Offline
Member
Joined: Oct 2003
Posts: 259
Arlington MA U.S.
Is there anything listed as far as grounding panel boards or cans that are mounted next to each other? I will be seeing him tommorow afternoon and will talk it over with him.

[This message has been edited by Joey D (edited 08-01-2005).]



Member Spotlight
togol
togol
NW In. USA
Posts: 421
Joined: September 2005
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.013s Queries: 14 (0.002s) Memory: 0.7766 MB (Peak: 0.9207 MB) Zlib enabled. Server Time: 2017-12-11 07:44:54 UTC