#54351 07/26/05 08:54 PM
Joined: Apr 2004
Posts: 811
Member
Quick question here guys. In a mobile home with a four wire feed from the pedestal, with the ground and neutral bonded at the pedestal, should the two be bonded in the service panel? I'm asking for my dad who can't use a 'puter.He asked an "electrician" (note the quotation marks), and he said that it's there in normal homes, and it should be in this house. This ain't a normal house.
Thank you,
Ian A.


Is there anyone on board who knows how to fly a plane?
Joined: Apr 2004
Posts: 811
Member
Also, are there any dangers of having the two bonded twice?

(Please excuse the stpid questions, I want more opinions.)
Ian A.


Is there anyone on board who knows how to fly a plane?
Joined: Jan 2005
Posts: 5,316
Cat Servant
Member
The "danger" in having the neutral and the ground connected to each other in more than one place is in that this set up a "parallel path." That is, part of the ground wire will always be carrying current- which it is not intended to do.
In a mobile home, connected by a cable, the risk is a lot less than, say, in a situation where a section of conduit becomes a "neutral;" but it is still aviolation.

Connect ("bond") the two once- preferably at the point where the utility neutral goes one way, and the wire to the ground rod goes the other.

As to things "always being done...." well, trailer/RV parks are famous for incorrect wiring methods.

Joined: Oct 2004
Posts: 55
R
Member
If the neutral is bonded at a second location away from where the grounding electrode conductor and the main bonding jumper connect, then there needs to be another ground rod driven and another equipment grounding conductor applied to the bonding jumper at the second location, just as if you were feeding a sub panel with the grounded conductor and the grounding conductor are run with the feeder. In the 2002 code book look at 250.32 for clarification. Although the pedestal does not constitute a separate building the intent is that for each point where the grounded conductor and the grounding conductor are bonded there is a separate connection to earth. What might be acceptable is to connect a separate grounding electrode conductor from the panel in mobile to the existing ground rod.

Joined: Oct 2000
Posts: 2,749
Member
See 550.16(A)(1) on page 451 in the 2005 NEC for the correct answer to the question.


Joe Tedesco, NEC Consultant
Joined: Mar 2005
Posts: 399
A
Member
Look at the outside of the home where the electrical connection goes under the home. Look for the sticker that may still be there. It will read something like 120 / 240 volt FOUR wire.
Follow the instructions.
If they were meant to be reconnected at the home it would only need three wires.
One "danger" of reconnecting is that the frame of the home is bonded to the grounding conductor. Connecting the green to the white wire in the home means you could energize the frame of the home.
Alan --


Alan--
If it was easy, anyone could do it.
Joined: Apr 2004
Posts: 811
Member
Sorry, but this place is so old (1973) the stickers are long gone! I know the home is four wire, since the electrician who serviced another home of the same model said he found a sticker that said:

120/240VAC
100Ampere
60Hz

"Connecting the green to the white wire in the home means you could energize the frame of the home." And the aluminum siding.

Ian A.

[This message has been edited by Theelectrikid (edited 07-27-2005).]


Is there anyone on board who knows how to fly a plane?

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Tom
Tom
Shinnston, WV USA
Posts: 1,044
Joined: January 2001
Top Posters(30 Days)
Admin 12
Trumpy 10
Popular Topics(Views)
280,350 Are you busy
213,425 Re: Forum
200,348 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5