#53623 06/30/05 06:52 PM
Joined: Feb 2002
Posts: 56
D
drgnz23 Offline OP
Member
I having a discussion with one of the older guys about conductors in a 1/2 conduit. I look it up in the code book but its kind of confusing. For example (SIMPLE) 1/2 emt only 9 thhn wires .Is one of those a ground?

#53624 06/30/05 06:55 PM
Joined: Nov 2000
Posts: 2,148
R
Member
The wire fill is a physical count of the wires in the raceway. What function the wires serve does not enter into this.
Don


Don(resqcapt19)
#53625 07/01/05 11:12 AM
Joined: Apr 2004
Posts: 349
Member
This information is based on Table 1 in Chapter 9 of the NEC, which specifies maximum raceway fill:

53% max for a single conductor in the raceway (i.e. - grounding conductor)
31% max for two conductors
40% for 3 or more conductors

The unused volume of air space within the raceway is needed for cooling of the conductors which tend to warm up due to conductor heating caused by current flow thru the circuit conductors. Overstuffing a raceway, aside from making for a difficult pull, would contribute to conductor overheating by reducing the cooling medium.