Expansion couplings for PVC service #53542 06/28/05 04:32 PM
Joined: Jun 2005
Posts: 124
P
poorboy Offline OP
Member
When am I required to use PVC expansion couplings...do I need them for the service I described in the PVC Service thread? I always use them at residential services on poles, but here I have block buildings and the 4" conduits come out of well compacted asphalt over gravel parking lot.

By the way, yes, I do have a code book...but you guys are just so darn accomodating.(LOL) Thanks for the input!

Work Gear for Electricians and the Trades
Re: Expansion couplings for PVC service #53543 06/28/05 08:50 PM
Joined: Feb 2005
Posts: 693
L
Larry Fine Offline
Member
Without looking it up, my instincts say only when crossing a structural expansion joint, or other joint subject to movement.

But then, I've been known to be wrong.


Larry Fine
Fine Electric Co.
fineelectricco.com
Re: Expansion couplings for PVC service #53544 06/28/05 09:11 PM
Joined: Jun 2005
Posts: 124
P
poorboy Offline OP
Member
I should clarify that I live in Maine and we use them when we think frost will move the ground a few inches. This solid compacted gravel seems unlikely to move a whole lot, however.

I have repaired meter trims that had 2" PVC driven up into the trim an inch by the frost action(Popped the concentric KO's right out) in mobilehome services on a pole.

Re: Expansion couplings for PVC service #53545 06/28/05 09:40 PM
Joined: Apr 2002
Posts: 7,121
HotLine1 Offline
Member
Poorboy:
My NEC is in my truck, but...
Any PVC exiting the ground should have an expansion joint.
Ground heaving and/or settlement causes a lot of damage.

Also, 'runs' of PVC on roofs, walls, etc., require exp. joints. There's a table in the Carlon catalog giving requirements, with amount of expansion, etc.

As said above, in large buildings, where there are structural expansion joints, it is required to install expansion joints on ALL raceways. (PVC, EMT, GRC, etc)

John


John
Re: Expansion couplings for PVC service #53546 06/28/05 09:50 PM
Joined: Jun 2003
Posts: 681
P
PCBelarge Offline
Member
In Maine you definitely need to be concerned about ground movement due to frost heave. 300.5(J) is the reference and you will need to use one of several approved methods.
Of course this is for conduit that is coming up from under the grade.
Read the FPN following this section.


Pierre Belarge
Re: Expansion couplings for PVC service #53547 06/28/05 11:41 PM
Joined: Jan 2005
Posts: 5,316
renosteinke Offline
Cat Servant
Member
Fascinating! I never thought about frost heave. I am lucky to live where the winters are somewhat milder than they are in the "rust belt," and our ground doesn't have much moisture in it to freeze- so it's not an issue here.
(Of course, the downside is you almost need dynamite to place a ground rod!)


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Attic Rat
Attic Rat
Bergen Co.,N.J. USA
Posts: 524
Joined: December 2003
Show All Member Profiles 
Top Posters(30 Days)
sparky 10
Popular Topics(Views)
259,540 Are you busy
194,935 Re: Forum
184,367 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3