300lb Light Fixtures #53395 06/22/05 10:33 PM
Joined: Apr 2002
Posts: 156
K
kinetic Offline OP
Member
Looking for some suggestions on supporting some heavy light fixtures(300lbs). The fixtures will mount flush with a grid ceiling. There is about a 4 foot gap betwen the grid and the roof line. The roof is framed with wooden trusses.

Work Gear for Electricians and the Trades
Re: 300lb Light Fixtures #53396 06/22/05 10:53 PM
Joined: Jan 2004
Posts: 615
J
Jps1006 Offline
Member
I would start by lag-bolting some unitstrut across the trusses to carry off several. Then threaded rod down to another strut at your desired elevation. Then figure a fastener that will meet up with the mounting bracket supplied by the fixture.
http://www.unistrut.com/

Re: 300lb Light Fixtures #53397 06/22/05 11:56 PM
Joined: May 2003
Posts: 2,876
E
e57 Offline
Member
Not often you'll see a heavy fixture in a grid cieling.

Anyway... Nice big heavy fixtures need something subtantial. Try spanning to structural framing with DEEEP strut, with horizontal anchoring via L brackets, and hanging the fixture via 1/2" rod. Good idea to add a safety cable too.

Good idea to get a good cut sheet of the fixture first.


Mark Heller
"Well - I oughta....." -Jackie Gleason
Re: 300lb Light Fixtures #53398 06/23/05 12:40 AM
Joined: Jul 2004
Posts: 9,513
G
gfretwell Offline
Member
You might want to talk to the structural inspector before you start hanging something heavy from a truss, particularly the bottom chord of a truss. He may want engineering.
YMMV on that but they get "funny" here about engineered assemblies. Maybe it is because the truss companies give inspectors free CEUs.
You will distribute the weight better if you span several with a 2x4 and "all thread" down from that.


Greg Fretwell
Re: 300lb Light Fixtures #53399 06/29/05 05:52 PM
Joined: Apr 2002
Posts: 156
K
kinetic Offline OP
Member
Thank you for the replies guys. The fixtures arrived yesterday and I had a chance to look at them today. Much closer to 120-150lbs. Makes my life alot easier.

I am going to use 4 1/4" superscrews with 3/8" rod attached to each. With 5 feet of strut bolted to the rod. Anyone had any problems with the superscrews? The Dottie catalog says they are rated for 1900lbs. of pull strength. Anyone have the pull strength rating for a 1/4" lag bolt into wood? I guess with wood it would have to be a mean average.

Re: 300lb Light Fixtures #53400 06/29/05 11:05 PM
Joined: Jan 2005
Posts: 109
L
livetoride Offline
Member
when I have to hang something heavy I try to spread the load over and much area a I can. Lag bolt can take a big vertical load but can cause sag in a single truss. Spread the load over several trusses and less sag. I also try to extend to a load bearing wall when I can. (Over kill is good) Solid strut is stiffer/better for heavy loads. Rod from shaky so cal.

Re: 300lb Light Fixtures #53401 07/01/05 12:30 AM
Joined: May 2003
Posts: 2,876
E
e57 Offline
Member
I'm always leary of supporting heavy objects with fastener vertically. Although the pulling tension rating of the fastener is 1900 LBS, whats the rating of the material, whats the rating of the material it is in. (I guess you had the same question. For wood, it depends on the wood... And , depends on conditions too, what if there is a flood, and it gets soggy, not that it would, but it could.) When you have the fastener horizontal to the load, you're then dealing with the shear strength of the fastener, and material, which most often will be much higher.


Just for refferance fixture supports need to be independant of the box for it.

I often say when explaining the extra work involved for hanging chandelliers, "You have to build it as if you could have sex hanging from it. Not that you would, or suggest that you do"

[This message has been edited by e57 (edited 07-01-2005).]


Mark Heller
"Well - I oughta....." -Jackie Gleason

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
dougwells
dougwells
kamloops BC Canada
Posts: 1,155
Joined: May 2003
Show All Member Profiles 
Top Posters(30 Days)
BigB 3
Popular Topics(Views)
268,560 Are you busy
202,952 Re: Forum
191,330 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3