AFCI and GFCI threshold #53042
06/15/05 11:41 PM
06/15/05 11:41 PM
B
BigB  Offline OP
Member
Joined: Mar 2004
Posts: 742
Tucson, AZ USA
Does anyone know the GFCI threshold on C/H AFCI breakers? Assuming they have GFCI protection built in. Would an AFCI serve as GFCI protection in a required location? (such as an outdoor receptacle tapped into a bedroom circuit).

Work Gear for Electricians and the Trades
Re: AFCI and GFCI threshold #53043
06/15/05 11:56 PM
06/15/05 11:56 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,373
Estero,Fl,usa
If I read the spec right this is 5MA protection and they say it provides GFCI protection http://www.eatonelectrical.com/unsecure/cms1/TB00500002E.PDF

It is page 27


Greg Fretwell
Re: AFCI and GFCI threshold #53044
06/16/05 07:16 AM
06/16/05 07:16 AM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
Most AFCIs have their ground fault trip set at 30 to 50 mA and are not suitable for use where GFCIs are required. There are AFCIs that have the ground fault trip set at 5 mA and those can be used where GFCIs are required.
Don


Don(resqcapt19)
Re: AFCI and GFCI threshold #53045
06/16/05 10:12 AM
06/16/05 10:12 AM
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
Call me a "doubting Thomas," but I am still cynical as regards AFCI products. Without regard to what the mfr claims, and considering the economy of GFCI devices, I would prefer to have a GFI receptacle where GFI protection is required.
The AFCI, however, has to be in (or real close) to the panel- which may be nowhere near the receptacle. Leads to a game of "hide and seek."

The code may require AFCI's, and the mfrs may claim wonders for them, but I will only tolerate them until there's some more of a track record for them.

In fairness, my cynicism is partly inspired by the "bait and switch" campaign pulled by the mfrs in getting these things into the NEC. That, however, is another thread.

Re: AFCI and GFCI threshold #53046
06/16/05 11:42 AM
06/16/05 11:42 AM
T
Tech-Home  Offline
Member
Joined: May 2005
Posts: 16
Burnsville, MN, USA
Do they make arc-fault receptacles? I have heard reference to them but have never been able to find any. Doesn't the code talk about the receptacle version someplace?

Re: AFCI and GFCI threshold #53047
06/16/05 01:26 PM
06/16/05 01:26 PM
R
Ryan_J  Offline
Moderator
Joined: Aug 2003
Posts: 1,374
West Jordan, Utah, USA
The 2005 talks about "devices", but doesn't specify receptacles. I am told that the devices being made right now are simply a faceless AFCI, with no receptacle, just a test and reset button.


Ryan Jackson,
Salt Lake City
Re: AFCI and GFCI threshold #53048
06/17/05 11:17 PM
06/17/05 11:17 PM
S
srssemass  Offline
Junior Member
Joined: Apr 2005
Posts: 6
Fall River, Ma, USA
My employer inquired and found that there were "no plans" on developing an Arc-fault recepticle by any major manufacturer.

Re: AFCI and GFCI threshold #53049
06/18/05 03:59 AM
06/18/05 03:59 AM
M
macmikeman  Offline
Member
Joined: Jul 2002
Posts: 717
Honolulu, Hawaii
The more I install them the more I like them. I believe I like them due to the gfi built into them. What I think I now see is what a great idea it would have been to require "coordinated ground fault circuit protection " on general purpose lighting and receptacle branch circuits all along since gfi's first were developed. When I say coordinated I mean like this - say for instance ground fault protection set at 200 milliamps at the service, 50 milliamps at branch circuit breakers, and a 5 milliamp requirement at all the current required places. I think any real fire stopping attibuted to ark fault breakers is because of the gfi portion of the device . The Industry would have been better served to go about this as a ground fault protection issue, rather than a promise of reducing fires which may or may not happen, but at least there would be less fresh fodder for attorney's to mine.

Re: AFCI and GFCI threshold #53050
06/18/05 02:06 PM
06/18/05 02:06 PM
C
CanadianSparky  Offline
Member
Joined: Mar 2001
Posts: 85
Alberta Canada
I may be wrong here but I think the purpose of AFCI was also to protect the integrity of the wiring and not just from the wallbox on. Thereby making AFCI receps. useless.

Re: AFCI and GFCI threshold #53051
06/18/05 05:11 PM
06/18/05 05:11 PM
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
Well, Canadian Sparky, you've identified the very point of controversy there.
AFCI's were first advertised as an answer to frayed cords and such. I even saw pics of AFCI receptacles.
Then, before their use became mandatory (and parts houses started carrying them), a slight change was made in the code wording, calling for protecting the entire circuit- and the devices disappeared. Now the press releases all spoke of the staple pinching the romex.

At that point, some folks began to feel they had been misled as to the purpose of the AFCI.

In the latest code (2005), there is a provision for using a device mounted near the panel to protect everything downstream from that point.

Having such a device will accomplish two things- allow you to add AFCI to circuits from an older (or obsolete) panel, and bring down the cost.

GFI Breaker $35
GFI Device $12

AFI Breaker $35
AFI device ?

It has been alleged that a breaker costs so much more than a device only because you have to go to one manufacturer for the breaker, while anybody's device will fit in the box.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Posts: 362
Joined: April 2003
Show All Member Profiles 
Top Posters(30 Days)
Admin 5
Popular Topics(Views)
257,129 Are you busy
192,961 Re: Forum
182,612 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.030s Queries: 14 (0.006s) Memory: 1.0121 MB (Peak: 1.1887 MB) Zlib enabled. Server Time: 2019-07-20 15:58:33 UTC