Is there a code that prohibits a gfi with in a certain distance from a lake? I'm asumming it's 10 feet like a pool.
Jesus may have been a capenter,but God was an electrician.Genesis1:3
|
|
|
|
Joined: Jul 2004
Posts: 9,988 Likes: 35
Member
|
Nope, you can have a receptacle on a pier over the lake. Same with salt water.
Greg Fretwell
|
|
|
|
Joined: May 2004
Posts: 162
Member
|
If the installation is near a body of water as stated check article 555 to determine elevations from the water datum plane if applicable 555.19 ect.
Charlie
|
|
|
|
Joined: Jul 2004
Posts: 9,988 Likes: 35
Member
|
note 555.1 says "Private, noncommercial docking facilities constructed or occupied for the use of the owner or residents of the associated single-family dwelling are not covered by this article."
You should still be aware of the artice though so you can make good "design" decisions.
Greg Fretwell
|
|
|
|
Joined: Oct 2000
Posts: 2,749
Member
|
See 682.15 in the 2005 NEC
Joe Tedesco, NEC Consultant
|
|
|