#6/2 NM Good for 65 amps? #52670 06/02/05 03:04 AM
Joined: Aug 2001
Posts: 545
A
aldav53 Offline OP
Member
The code book says #6 THHN is good for 65 amps. Is 6/2 NM considered THHN? Its not marked that. How many amps is 6/2 NM good for? At Home Depot they have 6/2 labeled rated at 50 amps. ??


The Golden Rule - "The man with the gold makes the rule"
Work Gear for Electricians and the Trades
Re: #6/2 NM Good for 65 amps? #52671 06/02/05 03:28 AM
Joined: May 2005
Posts: 10
P
plcnewbie Offline
Junior Member
check out 334.80 ampacity NM is 60 degree rated conductor

[This message has been edited by plcnewbie (edited 06-02-2005).]

Re: #6/2 NM Good for 65 amps? #52672 06/02/05 04:22 AM
Joined: Jan 2003
Posts: 4,391
I
iwire Offline
Moderator
Because of 334.80 6/2 NM is rated 55 amps.

With the use of 240.4(B) many times you can use a 60 amp breaker with 6/2 NM.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: #6/2 NM Good for 65 amps? #52673 06/02/05 11:56 PM
Joined: Aug 2001
Posts: 545
A
aldav53 Offline OP
Member
Couldn't find the code art. 6/2 NM is supposed to be 90 deg rated, which is the same as THHN, which would be 65 amps.


The Golden Rule - "The man with the gold makes the rule"
Re: #6/2 NM Good for 65 amps? #52674 06/03/05 12:56 AM
Joined: Jul 2004
Posts: 9,571
G
gfretwell Online Content
Member
334.80 Ampacity.
The ampacity of Types NM, NMC, and NMS cable shall be determined in accordance with 310.15. The ampacity shall be in accordance with the 60°C (140°F) conductor temperature rating. The 90°C (194°F) rating shall be permitted to be used for ampacity derating purposes, provided the final derated ampacity does not exceed that for a 60°C (140°F) rated conductor.


Greg Fretwell

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Posts: 362
Joined: April 2003
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
275,712 Are you busy
209,630 Re: Forum
196,972 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3