#52589 05/30/05 10:16 AM
Joined: Jul 2001
Posts: 311
Member
Is it somewhat accurate to say that "in general" fire alarm pull stations are wired in series and smoke detectors are wired in parallel for non-programmable systems?

[This message has been edited by Frank Cinker (edited 05-30-2005).]

[This message has been edited by Frank Cinker (edited 05-30-2005).]

#52590 05/30/05 10:53 AM
Joined: Jan 2003
Posts: 4,391
I
Moderator
No

Normally open non-addressable fire alarm devices such as smokes, pulls, heats etc. must be wired parallel.

Normally closed trouble indicators like tamper switches, pressure switches other panel trouble contacts etc. can be wired in series.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
#52591 05/30/05 01:44 PM
Joined: Feb 2005
Posts: 693
L
Member
A series circuit can be considered "self-monitoring" because a break (accidental or malicious) will have the same effect as an alarm condition.

A parallel circuit can be made "monitor-able" by using a termination resistor, as long as the monitoring panel is set up for the purpose.


Larry Fine
Fine Electric Co.
fineelectricco.com
#52592 05/30/05 07:32 PM
Joined: Jan 2003
Posts: 4,391
I
Moderator
Larry

Quote
A series circuit can be considered "self-monitoring" because a break (accidental or malicious) will have the same effect as an alarm condition.

I have never seen a fire alarm system circuit treat an open as an alarm event.

A open condition in the circuit causes a trouble.

A closed condition in the circuit causes an alarm.

A circuit with the proper resistance results in a idle panel. [Linked Image]


Bob Badger
Construction & Maintenance Electrician
Massachusetts
#52593 05/30/05 07:41 PM
Joined: Feb 2005
Posts: 693
L
Member
I was generalizing, as was Frank in the first post.

Some series-circuit systems do not see a difference between an alarm condition and a line break. Opening a circuit is opening a circuit.

"A open condition in the circuit causes a trouble."
In a parallel (N.O.) circuit with an end-of-line resistor, yes. In a N.C. circuit, that looks like a trip.

"A closed condition in the circuit causes an alarm."
In the aforementioned N.O. circuit, ditto. In a series circuit, a short is a bypass.

"A circuit with the proper resistance results in a idle panel."
Ditto again.

[Linked Image] Back at ya!

[This message has been edited by Larry Fine (edited 05-30-2005).]


Larry Fine
Fine Electric Co.
fineelectricco.com

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
dougwells
dougwells
kamloops BC Canada
Posts: 1,156
Joined: May 2003
Top Posters(30 Days)
Admin 11
Trumpy 10
Popular Topics(Views)
280,298 Are you busy
213,389 Re: Forum
200,330 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5