Fire Alarm Pull Station #52589 05/30/05 09:16 AM
Joined: Jul 2001
Posts: 311
F
Frank Cinker Offline OP
Member
Is it somewhat accurate to say that "in general" fire alarm pull stations are wired in series and smoke detectors are wired in parallel for non-programmable systems?

[This message has been edited by Frank Cinker (edited 05-30-2005).]

[This message has been edited by Frank Cinker (edited 05-30-2005).]

Work Gear for Electricians and the Trades
Re: Fire Alarm Pull Station #52590 05/30/05 09:53 AM
Joined: Jan 2003
Posts: 4,391
I
iwire Offline
Moderator
No

Normally open non-addressable fire alarm devices such as smokes, pulls, heats etc. must be wired parallel.

Normally closed trouble indicators like tamper switches, pressure switches other panel trouble contacts etc. can be wired in series.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: Fire Alarm Pull Station #52591 05/30/05 12:44 PM
Joined: Feb 2005
Posts: 693
L
Larry Fine Offline
Member
A series circuit can be considered "self-monitoring" because a break (accidental or malicious) will have the same effect as an alarm condition.

A parallel circuit can be made "monitor-able" by using a termination resistor, as long as the monitoring panel is set up for the purpose.


Larry Fine
Fine Electric Co.
fineelectricco.com
Re: Fire Alarm Pull Station #52592 05/30/05 06:32 PM
Joined: Jan 2003
Posts: 4,391
I
iwire Offline
Moderator
Larry

Quote
A series circuit can be considered "self-monitoring" because a break (accidental or malicious) will have the same effect as an alarm condition.

I have never seen a fire alarm system circuit treat an open as an alarm event.

A open condition in the circuit causes a trouble.

A closed condition in the circuit causes an alarm.

A circuit with the proper resistance results in a idle panel. [Linked Image]


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: Fire Alarm Pull Station #52593 05/30/05 06:41 PM
Joined: Feb 2005
Posts: 693
L
Larry Fine Offline
Member
I was generalizing, as was Frank in the first post.

Some series-circuit systems do not see a difference between an alarm condition and a line break. Opening a circuit is opening a circuit.

"A open condition in the circuit causes a trouble."
In a parallel (N.O.) circuit with an end-of-line resistor, yes. In a N.C. circuit, that looks like a trip.

"A closed condition in the circuit causes an alarm."
In the aforementioned N.O. circuit, ditto. In a series circuit, a short is a bypass.

"A circuit with the proper resistance results in a idle panel."
Ditto again.

[Linked Image] Back at ya!

[This message has been edited by Larry Fine (edited 05-30-2005).]


Larry Fine
Fine Electric Co.
fineelectricco.com

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
JoeKP
JoeKP
Berkley, MA
Posts: 144
Joined: March 2008
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 18
NORCAL 10
Popular Topics(Views)
274,310 Are you busy
208,151 Re: Forum
195,743 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3