#52589 05/30/05 09:16 AM
Joined: Jul 2001
Posts: 311
F
Member
Is it somewhat accurate to say that "in general" fire alarm pull stations are wired in series and smoke detectors are wired in parallel for non-programmable systems?

[This message has been edited by Frank Cinker (edited 05-30-2005).]

[This message has been edited by Frank Cinker (edited 05-30-2005).]

Horizontal Ad
#52590 05/30/05 09:53 AM
Joined: Jan 2003
Posts: 4,391
I
Moderator
No

Normally open non-addressable fire alarm devices such as smokes, pulls, heats etc. must be wired parallel.

Normally closed trouble indicators like tamper switches, pressure switches other panel trouble contacts etc. can be wired in series.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
#52591 05/30/05 12:44 PM
Joined: Feb 2005
Posts: 693
L
Member
A series circuit can be considered "self-monitoring" because a break (accidental or malicious) will have the same effect as an alarm condition.

A parallel circuit can be made "monitor-able" by using a termination resistor, as long as the monitoring panel is set up for the purpose.


Larry Fine
Fine Electric Co.
fineelectricco.com
#52592 05/30/05 06:32 PM
Joined: Jan 2003
Posts: 4,391
I
Moderator
Larry

Quote
A series circuit can be considered "self-monitoring" because a break (accidental or malicious) will have the same effect as an alarm condition.

I have never seen a fire alarm system circuit treat an open as an alarm event.

A open condition in the circuit causes a trouble.

A closed condition in the circuit causes an alarm.

A circuit with the proper resistance results in a idle panel. [Linked Image]


Bob Badger
Construction & Maintenance Electrician
Massachusetts
#52593 05/30/05 06:41 PM
Joined: Feb 2005
Posts: 693
L
Member
I was generalizing, as was Frank in the first post.

Some series-circuit systems do not see a difference between an alarm condition and a line break. Opening a circuit is opening a circuit.

"A open condition in the circuit causes a trouble."
In a parallel (N.O.) circuit with an end-of-line resistor, yes. In a N.C. circuit, that looks like a trip.

"A closed condition in the circuit causes an alarm."
In the aforementioned N.O. circuit, ditto. In a series circuit, a short is a bypass.

"A circuit with the proper resistance results in a idle panel."
Ditto again.

[Linked Image] Back at ya!

[This message has been edited by Larry Fine (edited 05-30-2005).]


Larry Fine
Fine Electric Co.
fineelectricco.com

Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
RonKipperDatacom
RonKipperDatacom
Kansas City, KS
Posts: 30
Joined: January 2013
Top Posters(30 Days)
Popular Topics(Views)
333,172 Are you busy
258,340 Re: Forum
239,914 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5