ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
How's all our Non-US folks doing?
by djk - 07/23/21 09:13 PM
Switched Receptacles -Top or Bottom?
by donles - 07/23/21 10:51 AM
Do You Travel?
by Bill Addiss - 07/20/21 04:26 PM
Backup Generator Done Right
by timmp - 07/18/21 12:20 PM
Square D "All-In-One" Panelboard
by Rachel - 07/16/21 04:57 AM
New in the Gallery:
OOPSIE!
OOPSIE!
by timmp, July 13
AT&T Office Thermostat, Summer
AT&T Office Thermostat, Summer
by timmp, July 13
Who's Online Now
0 members (), 27 guests, and 16 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#52237 05/23/05 12:47 PM
Joined: Oct 2004
Posts: 39
F
frankft Offline OP
Member
Today I opened up a panel and I saw a 12 awg neutral wire was very melted. I expected to see that a multiwire branch circuit had been miss wired but after tracing the wire back to the nm cable I saw that it was just a single wire circuit. The hot leg of this cable looked fine. I was wondering what would cause this to happen to only 1 conductor out of 20? I'll be going back next week to investigate more, after the homeowner takes down some sheetrock to expose some burried boxes! :-O In the meantime I disconnected the circuit from the breaker and I unconnected the neutral. Any Ideas?


Thats how we do it up in the woods!
#52238 05/23/05 01:07 PM
Joined: Jul 2002
Posts: 680
W
Member
Bad connection?? loose screw on neutral bar

#52239 05/23/05 01:47 PM
Joined: Oct 2004
Posts: 39
F
frankft Offline OP
Member
When I removed the melted wire, the terminal it was under was tight. Thanks for the reply.


Thats how we do it up in the woods!
#52240 05/23/05 04:37 PM
Joined: Jul 2004
Posts: 145
C
Member
I am thinking (especially with you mentioning buried boxes) that the neutral may possibly have been commoned with other neutrals in one of the boxes, thus acting as the return for other circuits too. It's at least a possibility.

#52241 05/23/05 05:11 PM
Joined: May 2003
Posts: 2,876
E
e57 Offline
Member
I'm with chipmunk on this. Although you see a 2-wire in the panel, it could be carrying 2 or more loads. Especially bad if they are the same phase. Good way to find out is to put an amp-clamp on it, check the load amps, shut the circuit off, and check again. Another is to shut the whole house off, and ring it out through all of the other circuits with the neutral disconnected. In both ways you could still miss it if the load were not on. The sure fire way is to follow it.

Other possibilities could be, and should not be ruled out, is that the breaker is bad, and it fed several space heaters for a while without tripping. The circuit could have a history of abuse, reset and trip cycles, or one big short in the past. Bad connection further in the circuit, or just plain dirty wire. (Dissimular metal, or chemical reaction, or low grade copper, or buss material.)


Mark Heller
"Well - I oughta....." -Jackie Gleason
#52242 05/23/05 06:57 PM
Joined: Oct 2004
Posts: 39
F
frankft Offline OP
Member
Thanks Chipmunk and e57. I hope I'll see the problem when they open up the ceiling. I told the home owner that since the neutral was melted in the panel, that we could assume that it is melted in other parts of the circuit also. My thoughts are leaning towards finding some neutrals from different circuits tied together. Thanks again.


Thats how we do it up in the woods!
#52243 05/23/05 08:59 PM
Joined: Aug 2002
Posts: 7
J
Junior Member
Funny. No one asked if you ampprobed the noodle. I would have amprobed the hot, then ampprobed the n. This can tell you what is going on..... and also where to start looking


john
#52244 05/23/05 09:19 PM
Joined: May 2002
Posts: 1,716
R
Member
John, you really need to post more often. [Linked Image]

I would add that if you would clamp around both the ungrounded and grounded conductor at the same time and the meter reads anything besides zero, we would have a problem if it was suspect of being a two wire circuit.

Roger


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
sparky66wv
sparky66wv
West Virginia
Posts: 2,236
Joined: November 2000
Top Posters(30 Days)
timmp 4
Rachel 4
Popular Topics(Views)
281,407 Are you busy
215,050 Re: Forum
201,934 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5