ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Mini Split voltage
by Garemaret - 06/21/24 04:53 AM
Strobing LEDs
by Anovalight - 06/20/24 03:16 AM
Stuff that happens after we leave
by HotLine1 - 06/17/24 03:53 PM
photocell requirement for metal halide ballasts
by gfretwell - 06/17/24 01:44 PM
Commercial lift stations
by triple - 06/09/24 05:23 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 53 guests, and 9 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#52114 05/19/05 02:58 PM
Joined: Jul 2002
Posts: 241
S
SJT Offline OP
Member
We have a 225kva transformer, with 480v primary and 208 sec. The installation the way it is now, has 2 - 4" seal tights, each going to a 400amp switch. Are you allowed 2 diffrent disconnects on the secondary side? Do the secondary conductors have to terminate into a single switch or breaker? Such as a 600 amp main breaker panel? Can they end up into 2 switches?
Thanks

#52115 05/19/05 04:09 PM
Joined: Mar 2003
Posts: 849
Y
Member
Is this in a Superivised Industrial site or not?? (240.2) definitions.If so read 240.90 if not read 240-21c.

#52116 05/20/05 02:57 PM
Joined: Jul 2002
Posts: 241
S
SJT Offline OP
Member
Thanks for the input


Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5