Grounding of two prong system. #52005
05/18/05 12:40 AM
05/18/05 12:40 AM
E
Edward  Offline OP
Member
Joined: Dec 2002
Posts: 308
California
What are your thoughts on this?
Customer wants me to provide grounding for the two prong receptacles. i highly suggest running two bare copper under the house and tie each grounding conductor from each receptacle to that. He says my plumbing is copper i want you to tie on to that. I really do not like that route because i do not know what will happen to the plumbing after i leave.

Please give me your thoughts. would you use the plumbing to provide grounding for the receptacles?

Thanks
Edward


Thanks
Edward
Work Gear for Electricians and the Trades
Re: Grounding of two prong system. #52006
05/18/05 12:51 AM
05/18/05 12:51 AM
D
dmattox  Offline
Member
Joined: Oct 2004
Posts: 265
Anaheim, CA
The code allows you to replace ungrounded receptacles with a GFI. Going to the copper plumbing pipe is a violation.

Re: Grounding of two prong system. #52007
05/18/05 12:56 AM
05/18/05 12:56 AM
E
Edward  Offline OP
Member
Joined: Dec 2002
Posts: 308
California
Thanks dmattox.
I know about the GFCI replacement. But i personally do not like GFCI look all over the house. Can you reference the nec section on the violation if bonded plumbing is being used. So i will learn.

Thanks


Thanks
Edward
Re: Grounding of two prong system. #52008
05/18/05 05:40 AM
05/18/05 05:40 AM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Here are your options for adding a grounding conductor to the circuits.

Quote
250.130(C) Nongrounding Receptacle Replacement or Branch Circuit Extensions. The equipment grounding conductor of a grounding-type receptacle or a branch-circuit extension shall be permitted to be connected to any of the following:

(1)Any accessible point on the grounding electrode system as described in 250.50

(2)Any accessible point on the grounding electrode conductor

(3)The equipment grounding terminal bar within the enclosure where the branch circuit for the receptacle or branch circuit originates

(4)For grounded systems, the grounded service conductor within the service equipment enclosure

(5)For ungrounded systems, the grounding terminal bar within the service equipment enclosure


250.130(C)(1) allows the connection to the water pipe however it would have to be within 5' of the point of entrance per 250.52(A)(1).


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: Grounding of two prong system. #52009
05/18/05 07:16 AM
05/18/05 07:16 AM
W
winnie  Offline
Member
Joined: Sep 2003
Posts: 649
boston, ma
To help educate your customer, you might add that grounding to the water pipes _used_ to be allowed (the 5 foot restriction that iwire mentions is relatively new), but because of the very real chance that plastic pipe will be used in modern repairs, water pipes can now only be used in 5 foot section described.

You also may want to consider that running a new equipment grounding conductor is nearly as much effort as running new romex over the same distance, and given that this is old work, probably a T+M job. I'd strongly consider estimating the cost difference between running new ground conductors versus simply running new circuits.

-Jon


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
electure
electure
Fullerton, CA USA
Posts: 4,280
Joined: December 2000
Show All Member Profiles 
Top Posters(30 Days)
Khombo 2
Popular Topics(Views)
255,764 Are you busy
191,731 Re: Forum
181,497 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.022s Queries: 14 (0.004s) Memory: 0.9691 MB (Peak: 1.1086 MB) Zlib enabled. Server Time: 2019-06-20 03:33:46 UTC