Help me to properly understand the 220.19 table for computing the demand factor for a 11KVa stove. Do you multiply 11,000 x 8 = 880 or do you figure it 8 x 1000 = 8,000? Not sure if I'm doing it right.

Thanks

Joined: Feb 2002
Posts: 182
B
Bob Offline
Member
Read note 2 under the table. It explains the prodeedure.

Joined: Mar 2005
Posts: 88
J
JFLS41 Offline OP
Member
I read that, still scratching my head... care to explain if you don't mind?

thanks

Joined: May 2002
Posts: 1,716
R
Member
When using column C the math is already done. (1) 11kw range = 8kw, or 8 x 1000 as you said.

Roger

[This message has been edited by Roger (edited 04-26-2005).]


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
SafetyWired
SafetyWired
Pa, USA
Posts: 44
Joined: July 2013
Top Posters(30 Days)
Trumpy 10
Admin 10
Popular Topics(Views)
280,437 Are you busy
213,510 Re: Forum
200,399 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5