Hello everyone, Got a question I hope you can help me with. My brother just got some machinery from japan that we need to put plugs on. The 220volt machines have the following colored wires in the cord: green/yellow, brown, and blue. Which one of these wires is the ground. I would say the green/yellow but want to make sure. Thanks for the help..........Jim
|
|
|
|
Joined: Sep 2004
Posts: 93
Member
|
Green/yellow = earth/ground.
Brown = live (hot) Blue = Neutral.
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
Jim, I agree with jooles color code.
I just want to add that when in doubt a simple continuity test from the machinery's electrical enclosure to the conductors in the cord will determine the true grounding conductor.
Bob
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
Joined: Jul 2004
Posts: 10,006 Likes: 37
Member
|
The blue shows up in 400.22(C)
[This message has been edited by gfretwell (edited 04-24-2005).]
Greg Fretwell
|
|
|
|
Joined: Jan 2005
Posts: 5,476 Likes: 3
Cat Servant Member
|
And- if the machine has receptacles mounted on it- they will be only 100 volts...even if it looks like a standard receptcal!
|
|
|
|
Joined: May 2002
Posts: 1,716
Member
|
From Umagooma,
umagooma New Member posted 04-24-2005 01:56 PM -------------------------------------------------------------------------------- Thanks everyone for the quick replies! I do agree to take a continuity test but the machines are at my brothers house half way across N. Caroilna. He is getting a qualified person to hook this up for him but I just wanted to check here for myself. I forgot to mention that these machines are rated 220volts(5.6 amps) and are from China, not Japan. They are mixers for ink as he is a color chemist and will be using these mixers to come up with colors. Thanks for all the help..Jim
[This message has been edited by Roger (edited 04-24-2005).]
|
|
|
|
Joined: Apr 2005
Posts: 2
OP
Junior Member
|
Sorry Roger and thanks, will do...Jim
|
|
|
|
Joined: May 2002
Posts: 1,716
Member
|
Jim, no appology needed, and you're welcome.
Roger
|
|
|
|
Joined: Aug 2001
Posts: 7,520
Member
|
This color code is now the standard on appliance cords throughout almost all of Europe, as well as many other countries, including Australia and New Zealand.
In fact brown, blue, green/yellow is virtually the standard system now for anywhere outside the American and Japanese spheres of influence.
|
|
|
|
Joined: Mar 2005
Posts: 1,803
Member
|
Same color codes in France on domestic single phase equipment= green/yellow for ground (earth), blue always for neutral and brown for hot (live). I have an idea that these colors were chosen because of possible color-blindness by end users. However, in house wiring here there are a lot of old 3-phase house installations, or single phase conversions from 3-phase. ANY color other than blue must therefore be considered a possible 'hot', and a real problem is DIY Brits' wiring neutrals in black in French houses and baffling French electicians. Paul- Question- wouldn't the importer have to ensure compliance with US standards on equipment in order to bring it into the United States- similar to the European CE mark? Alan
Wood work but can't!
|
|
|
Posts: 44
Joined: August 2005
|
|
|
|