Photo of the Week:
Mouse on a Bus
Mouse on a Bus
0 members (), 121 guests, and 20 robots.
#50407 04/01/05 04:19 PM
Are all circuits leaving a panel board, protected by breakers considered branch circuits only?
Or Feeders also?
#50408 04/01/05 04:27 PM
Circuits leaving a panel can be either branch circuits or feeders.
Branch Circuit. The circuit conductors between the final overcurrent device protecting the circuit and the outlet(s).
Feeder. All circuit conductors between the service equipment, the source of a separately derived system, or other power supply source and the final branch-circuit overcurrent device.
#50409 04/01/05 06:22 PM
So if a main panel houses a 60a breaker feeding a main lug sub, the conductors between the 60a breaker and the sub-panel are feeders.
#50410 04/01/05 06:40 PM
But, it's not necessarily a "feeder" for purposes of Table 310.15(B)(6).
YMMV.
#50411 04/01/05 07:18 PM
Why would it not necessarily be a feeder? Are you saying it would be a service conductor(s) if this was a separate building? Please elaborate.
#50412 04/01/05 07:49 PM
I'll refer you to this discussion about 310:15(B)(6):
https://www.electrical-contractor.net/ubb/Forum2/HTML/001450.html
#50413 04/01/05 08:30 PM
Thanks, that was exhausting but I guess I asked for it.
Tools for Electricians
2023 NEC + Exam Prep Study Guides Now Available!
Bill Addiss
Bill Addiss
NY, USA
340,322 Are you busy
265,714 Re: Forum
246,723 Need opinion
