ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Look Ma! I Did It Myself!
by renosteinke - 12/04/23 02:57 AM
Scary Looking Receptacles
by renosteinke - 12/04/23 02:46 AM
Old Computers?
by gfretwell - 11/21/23 03:45 PM
Simplify MOSFET Test With Source Measure Meter
by gfretwell - 11/18/23 09:20 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 12 guests, and 12 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#50338 03/30/05 07:27 PM
Joined: Dec 2004
Posts: 6
S
Junior Member
I have 1 exhaust fan for a house. This fan is ducted for the bathrooms and whole house fan. I have 3 timers for which it can be started from. 2 will be located in bathrooms and 1 in laundry room with a 24hr timer. How would this be accomplished? The 2 bathroom timers will be a pushbutton type so they can choose 10 min, 15, 30 etc.

I would imagine the fans would be wired similar to a 3 way - 4way - 3 way switch?

3 timers 1 fan.

Thanks guys

Mike

#50339 03/30/05 08:14 PM
Joined: May 2002
Posts: 1,716
R
Member
Mike, just wire the timers in parallel, this will let the selected timer{s} operate the fan for the duration of the longest timer setting that is in use.

Roger

#50340 03/30/05 08:36 PM
Joined: Oct 2002
Posts: 482
Z
Member
I agree with Roger, as I just installed one of these last week with several remote switch locations.

This is a simple two-wire hook up. At each switch/timer location, you have a power wire in and a traveler out (back to the fan). When any one of these switches/timers is closed, the fan activates. You can have infinate single pole/single throw switches/timers installed in parallel on the circuit.

Good Luck!

#50341 03/31/05 06:33 AM
Joined: Aug 2001
Posts: 332
S
Member
Sexton the prob with your 3way/4way hook up is that guy in bathroom "A" turns it off while the guy in bathroom "B" still wants it on. The parallel hook up allows it to stay on if any of the 3 turn it on. The only prob is that if you use switches instead of timers and it's left on you have to go looking for the swithch that turned it on. (I learned that the hard way).

#50342 03/31/05 10:47 PM
Joined: Nov 2004
Posts: 138
C
Member
Funny. We had 2 bathrooms back to back in an office building, and the duct guys set up one fan for both. So the guys in charge decided to hook up 3 ways. Pretty funny if you ask me...a brand new doctor's office.


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
BEAMEUP
BEAMEUP
WA
Posts: 27
Joined: December 2004
Top Posters(30 Days)
NORCAL 1
Popular Topics(Views)
313,348 Are you busy
239,239 Re: Forum
222,992 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5