ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Upside Down ThreeWay
by gfretwell - 08/12/22 12:30 AM
Load Calcs for EVs and RVs
by gfretwell - 08/12/22 12:24 AM
Wiring method choice
by HotLine1 - 08/10/22 03:39 PM
NEC- 314.23 (H) (1)
by renosteinke - 08/10/22 11:13 AM
RV Forums
by gfretwell - 08/07/22 07:01 PM
New in the Gallery:
240/208 to a house
240/208 to a house
by wa2ise, October 9
Now you know.
Now you know.
by Tom_Horne, September 7
Who's Online Now
0 members (), 22 guests, and 23 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Joined: Aug 2004
Posts: 69
N
nov Offline OP
Member
I need to replace 7 two prong outlets they are feed with two wire BX, but somewhere the BX is feed from knob and tube so no ground. Dont they make a gfci for this situation?

Joined: Dec 2003
Posts: 751
E
Member
2002 NEC: "406.3(D) Replacements. Replacement of receptacles shall comply with 406.3(D)(1), (2), and (3) as applicable.
(1) Grounding-Type Receptacles. Where a grounding means exists in the receptacle enclosure or a grounding conductor is installed in accordance with 250.130(C),
grounding-type receptacles shall be used and shall be connected to the grounding conductor in accordance with 406.3(C) or 250.130(C).
(2) Ground-Fault Circuit Interrupters. Ground-fault circuit-interrupter protected receptacles shall be provided where replacements are made at receptacle outlets that are required to be so protected elsewhere in this Code.
(3) Nongrounding-Type Receptacles. Where grounding means does not exist in the receptacle enclosure, the installation shall comply with (a), (b), or (c).
(a) A nongrounding-type receptacle(s) shall be permitted to be replaced with another nongrounding-type receptacle(s).
(b) A nongrounding-type receptacle(s) shall be permitted to be replaced with a ground-fault circuit interrupter type of receptacle(s). These receptacles shall be marked “No Equipment Ground.” An equipment grounding conductor shall not be connected from the ground-fault circuitinterrupter-type receptacle to any outlet supplied from the
ground-fault circuit-interrupter receptacle.
(c) A nongrounding-type receptacle(s) shall be permitted to be replaced with a grounding-type receptacle(s)where supplied through a ground-fault circuit interrupter.
Grounding-type receptacles supplied through the ground fault circuit interrupter shall be marked “GFCI Protected” and “No Equipment Ground.” An equipment grounding
conductor shall not be connected between the grounding type receptacles."


Earl
Joined: Dec 2003
Posts: 751
E
Member
Also, the armor of old style AC or BX (without the aluminum bonding strip) is not recognized as an equipment grounding means, and in reality on longer runs the armor's resistance is not low enough to trip the breaker if a dead short occurs. If your old house has this kind of AC, then I guess you need to feed the circuit with a GFCI breaker, or find the first receptacle and install a GFCI receptacle there, and wire the rest from "load". Don't forget the stick-on markers.


Earl
Joined: Aug 2001
Posts: 329
S
Member
Short answer:
1) if no ground exists put in a gfci at first recep and feed thru. Leave ground screw empty. You can use 2 or 3 prong receps for the rest of the ckt. Be sure to put stickers on downstream receps. or
2) install new 2 prong receps every place that's ungrounded and forget the gfci


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
dougwells
dougwells
kamloops BC Canada
Posts: 1,157
Joined: May 2003
Top Posters(30 Days)
BigB 5
Popular Topics(Views)
295,021 Are you busy
226,689 Re: Forum
211,858 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5