EMC Glands on Motors
by Trumpy - 12/01/22 06:12 AM
Ground Rods: Installation and Hook-Up
by Trumpy - 12/01/22 05:54 AM
Happy Thanksgiving all!
by gfretwell - 11/30/22 05:55 PM
Colt Firearms Switchbox
by NORCAL - 11/29/22 01:04 AM
Perfect work light?
by gfretwell - 11/22/22 12:48 AM
240/208 to a house
240/208 to a house
by wa2ise, October 9
Now you know.
Now you know.
by Tom_Horne, September 7
1 members (Scott35), 23 guests, and 26 robots.
#49579 03/10/05 09:11 AM
AJA Offline OP
I have an engine drive 22kw induction 3 phase generator, commercially made, which will not generate any voltage. It has been flashed while turning at rated speed and above with 12 and 24 vdc without results. The generator has been removed for the engine and been flashed with the 12 vdc which has pulled the rotor to the field coils. After assembly the unit still does not produce voltage. All help is appreciated.
Thanks
AJ
#49580 03/11/05 08:38 AM
AJ,
A little more info would help, there are several ways to make a field. If flashing your field does not produce a voltage, you likely have a bad set of diodes, or something broken/burned in the field. If you've got brushes - replace 'em THEN flash. Is there a fuse in the exciter you missed?
#49581 03/11/05 08:43 AM
May seem like a stupid suggestion but, have you buzzed the windings? I know checking for continuity seems pretty basic but hey gotta look at all scenarios.
#49582 03/11/05 08:47 AM
You din't say but have you verified that the exiter is operating correctly or at all?
#49583 03/14/05 07:29 AM
AJA Offline OP
The engine speed has be verified by two difference instruments. The windings provided the correct curve form on a scope. The rotor is laminated material and has no exciter circuit/no diodes. There were no capacitors with the unit.
AJ
Tools for Electricians
2023 NEC Now Available!
2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman
pcsailor
pcsailor
Minneapolis, MN, USA
Trumpy 9
NORCAL 3
300,576 Are you busy
230,190 Re: Forum
214,996 Need opinion
