"AHJ says if grounding elctrode conductor is longer then 100' up size from #4 to a #2." no code was refferanced.
Why? what would he be thinking? has any one seen this in nec 2002 or 2005?
|
|
|
|
Joined: Feb 2002
Posts: 182
Member
|
This is not a code problem. Its an engineering problem. If the grounding conductor is too long the impedance may cause a delay in the opening of the breaker. The 100 ft is a rule of thumb. To know if there is a problem you would need to caculate the fault current and check the curves for the breaker. How long is the conductor?
|
|
|
|
Joined: Oct 2004
Posts: 72
OP
Member
|
Are rules of thumb enforceable violation? NEC says nothing about rules of thumb, right? article 250 said nothing about it. is something wrong with 250.66? No
it's a residence with a 200amp service 4/0 alum grounding electrode conductor from service to with in 5' of whare water enters the house. a distance of 85'.
|
|
|
|
Joined: Oct 2004
Posts: 72
OP
Member
|
check the curves for the breaker? how do i do that? what is the curve of a breaker? are they like a womans curves?
|
|
|
|
Joined: Feb 2002
Posts: 375
Member
|
bucketman ---
The AHJ is asking you to either increase the conductor size or provide engineering showing your size is correct.
While the code may be silent on the issue, I think he is within the spirit of the code.
|
|
|
|
Joined: Oct 2004
Posts: 72
OP
Member
|
250.66 doesn't seem vary silent. it seems to be directly to the point. now I've been doen these service changes for a few years and never had the AHJ call me on the 80 some feet of ground condutor be to long. i just can't see the AHJ call me for something thats not in the code.
|
|
|
|
Joined: May 2002
Posts: 1,716
Member
|
Bucketman, I agree with you, as far as the GEC there is no restriction to length as you have said and in fact if the #4 GEC is bare it becomes part of the "Electrode" and the GE's function won't be improved to any great performance level by increasing the conductor size.
With this length of #4 copper in the ground, and if we were talking about a rod, the conductor would probably provide more of a GE than the rod itself.
Bob, the GE and GEC would play no part in the operation of an overcurret device.
Roger
[This message has been edited by Roger (edited 03-02-2005).]
|
|
|
|
Joined: Aug 2003
Posts: 1,374
Moderator
|
I think the AHJ is acting well beyond the scope of his/her authority.
Ryan Jackson, Salt Lake City
|
|
|
|
Joined: Oct 2004
Posts: 72
OP
Member
|
ya, talked to the AHJ to day befor I ripped out all that #4 and he said it was just a consern of his that it be up sized. So the #4 stands...
But next time I'll just pull #2 because its cool. I do think it's a good wiring practice and a good Idea and it cant heart but the $$$.
"I think the AHJ is acting well beyond the scope of his/her authority."
That was my hole thought. It was a you can't make me thing.
thanks all for the posts. keepem comen.
|
|
|
|
Joined: Feb 2002
Posts: 375
Member
|
1) It is not clear that the GEC is in the ground. I assumed it was not.
2) If there are no real concerns about the length, then the diameter does not matter. And we would not have a table of GEC related to service conductor.
The code is silent on the issue of maximum length of the GEC before meeting the grounding electrode.
|
|
|
Posts: 362
Joined: April 2003
|
|
|
|
|