ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat Box
Recent Posts
Fuse blower plug?
by HotLine1 - 08/20/19 01:50 PM
100 year old Light Bulb
by HotLine1 - 08/20/19 01:26 PM
Forum Updates Coming Soon.
by Admin - 08/18/19 01:55 PM
Anybody Remember this?
by Bill Addiss - 08/17/19 09:07 PM
1897 paper on 110-220 incandescent lamps
by ghost307 - 08/15/19 10:31 AM
New in the Gallery:
What is this for?
Plug terminals
Who's Online Now
0 registered members (), 13 guests, and 11 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 1 of 2 1 2
Running home runs next to pipes #48902 02/22/05 09:40 PM
Joined: Nov 2004
Posts: 138
C
Clydesdale Offline OP
Member
is it ok to snake wires in along side plumbing pipes? one of the pipes is for hot water..not for baseboard heat, but for shower. do i need to derate for higher ambient temp?

Work Gear for Electricians and the Trades
Re: Running home runs next to pipes #48903 02/22/05 09:55 PM
Joined: Jul 2002
Posts: 8,262
Trumpy Offline
Member
It may only be me, but I wouldn't put a cable anywhere near a water pipe, Hot or Cold.

Re: Running home runs next to pipes #48904 02/22/05 10:22 PM
Joined: Nov 2004
Posts: 138
C
Clydesdale Offline OP
Member
good to know. i will probably cut a channel in the plaster then. thanks

Re: Running home runs next to pipes #48905 02/23/05 12:19 AM
Joined: Aug 2004
Posts: 34
H
highkvoltage Offline
Member
Clydesdale. There is nothing wrong with running your conduit beside a water pipe. In fact on many commerical and industrial jobs you share pipe racks with the plumbers to conserve room. As far as a hot water pipe affecting the ambient temp of your conductors also not a problem. If this was a steam pipe i would still share the rack I would just add more space between them.

Re: Running home runs next to pipes #48906 02/23/05 05:36 PM
Joined: Nov 2004
Posts: 138
C
Clydesdale Offline OP
Member
highkvoltage, the wires will not be in conduit. they will be romex and would follow the pipes from the basement to the second floor because there is a space there next to the pipes(and will probably be touching them along the way quite a bit as i have no way of keeping the wires away from the pipes since the plaster is finished). the reason i wanted to do it this way is because i wanted to avoid cutting a channel from the first floor all the way up in to the attic so i can get new home runs up there for the second floor. the wiring is currently knob and tube and needs replacing. still think it's ok? is there another type of wire that can/should be used here?(UF?)

[This message has been edited by Clydesdale (edited 02-23-2005).]

[This message has been edited by Clydesdale (edited 02-23-2005).]

Re: Running home runs next to pipes #48907 02/23/05 06:07 PM
Joined: Dec 2003
Posts: 886
H
hbiss Offline
Member
Ok, so what you have is a pipe chase from the basement to the second floor and you want to fish some NM up through it.

I've done it but I don't like it. Don't like the idea of pvc jacketed cable in contact with a hot water pipe. UF wouldn't be any different would it.

If you can't insure that they will not contact the hot water pipe I would be more comfortable with AC or MC and it's metallic armor. I really don't think it's worth cutting up the plaster for this though.

-Hal

Re: Running home runs next to pipes #48908 02/23/05 06:35 PM
Joined: Jan 2002
Posts: 1,457
E
Electricmanscott Offline
Member
I don't see a problem with this. I have done this countless times and it is standard procedure around here as there are many two/three story houses. I don't see a hot water pipe causing any dammage. For what it's worth in renovations I have removed wiring that has been installed like this for many years with no signs of problems.

Re: Running home runs next to pipes #48909 02/23/05 06:49 PM
Joined: May 2004
Posts: 697
D
Dave55 Offline
Member
I don't see a problem with this either. The insulation is 90 degree? That's 190+ F (hot water is less), the term "leaky old house" probably applies, and a hole from the basement to the attic will have "chimney effect" air-flow.

Dave

Re: Running home runs next to pipes #48910 02/23/05 07:02 PM
Joined: Aug 2004
Posts: 34
H
highkvoltage Offline
Member
OK. Run the romex next to it. Either way not a code violation nor will it hurt the wire. Water pipes just don't get that hot.

Re: Running home runs next to pipes #48911 02/23/05 09:10 PM
Joined: Jan 2002
Posts: 1,457
E
Electricmanscott Offline
Member
Do yourself (or the next guy) a favor and leave a pull string. I ususally use some thhn. Oh wait. I don't think that it's listed to be used as a pull string. Doh!

Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
renosteinke
renosteinke
Blue Collar Country
Posts: 5,316
Joined: January 2005
Show All Member Profiles 
Top Posters(30 Days)
Admin 21
GeneSF 8
Popular Topics(Views)
257,889 Are you busy
193,624 Re: Forum
183,243 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3