Has anybody heard anything about new codes reguarding 3" hubs to a residential load center? Anybody have details??? Have heard it might be for panels 400A and up.
I have not heard anything. 310.15(B)(6) allows 400 KCMIL THWN copper for a 400 amp dwelling service. You could go traditional and use 500 KCMIL THWN, both fit in 2 1/2 per Annex C - Table C1 EMT and C4 IMC. In table C8 for RMC, 500 KCMIL would have to be in 3 inch.